Orthogonal Load Combinations for Seismic Drift Calculation

Orthogonal Load Combinations for Seismic Drift Calculation

Orthogonal Load Combinations for Seismic Drift Calculation

(OP)
I know this has been brought up on here before, but I couldn't really find a consensus. If the orthogonal load combinations are required for seismic design, are they also used for seismic drift computation as well? Thanks in advance.

RE: Orthogonal Load Combinations for Seismic Drift Calculation

(OP)
I'm referring to the 100/30 combinations when I say orthogonal load combinations. Sorry if I was unclear.

RE: Orthogonal Load Combinations for Seismic Drift Calculation

I believe that is the intent of ASCE 7-05 (and ASCE 7-10) but it is not specifically addressed in the Standard to the best of my knowledge. It doesn't make sense to me to use the orthogonal loading pattern for strength and use something different for drift.

RE: Orthogonal Load Combinations for Seismic Drift Calculation

Mike - I assume you are referring to ASCE 7-10 section 12.5.3a where it says:
"The requirement of Section 12.5.1 is deemed satisfied if members and their foundations are designed for 100 percent of the forces for one direction plus 30 percent of the forces for the perpendicular direction."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources