Perimeter Beams Panel Load

Perimeter Beams Panel Load

Perimeter Beams Panel Load

(OP)
Hi
For the perimeter beams design in PT slab, what is the slab panel width that those beams should take. In here standard practice is to take 1 or 2 m of slab panel load. In Singapore code it is stated that if marginal beams' depth is 1.5 times greater than the slab thickness, one quarter of the panel load need to be considered. If so is it double taking the loadings as we already considered the full panel load in slab design? I understand that the beams will still attract the panel loads because of its stiffness.
 
Is it possible not to double take the loading?

Thanks

RE: Perimeter Beams Panel Load

It is not necessary to design for double the load, but the perimeter beam will tend to hog the load from the slab, so you need to decide how to distribute the load between the two and adjust the slab reinforcement accordingly. In case of doubt, be conservative.

BA

RE: Perimeter Beams Panel Load

Thanks BA
But how to adjust the reinforcement? Reduce the reinforcement that joining slab and beam?

RE: Perimeter Beams Panel Load

Struggle,

I assume you are talking about perimeter beams parallel to the spanning direction of a one way slab!

With a significant beam/slab depth ratio, the slab bottom reinforcement within about 1-2m of the beam (within the effective flange width) will not actually increase in tension due to bending as the T beam will be effective in this width.

So the T beam needs to be designed for the load it will attract. 25% is probably a good approximation of this for a square grid of columns (about the amount that an edge beam in a 2way edge supported slab would attract)!

Normally the slab reinforcement is extended full width for simplicity.


RE: Perimeter Beams Panel Load

Thanks Gil
I am clear now. So perimeter RC beams will be designed with 25% of transverse panel load. What about PT slab parallel to those beams still need to take full panel load? Can I reduce the strands and reinforcement inside those beams effective flange? Anyway not to double take the loading?

What about two-way. Is it the same concept?

RE: Perimeter Beams Panel Load

Hi
Is up-stand perimeter beam an solution?
Thanks

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources