Good morning,
I am looking through project's scope of work and it says the removal and re-installation of thermocouples.
We are going to install a new secondary superheater ( 2 headers and 90 new elements ) and I was wondering how the thermocouples are normally attached and what type of NDE would be required for them ? It is my understanding that they are normally fillet/tack welded on to the tubes. I requirements in ASME Sec.1 in the PWHT section under P5A and it mentions capacitor discharge welding or electric resistance welding. I have never seen either of those processes performed before. Are there alternate NDE requirements / PWHT if you use SMAW or GTAW to weld them on ? It sounds like I need to get the design and location of these TC's from the engineer.
I am looking through project's scope of work and it says the removal and re-installation of thermocouples.
We are going to install a new secondary superheater ( 2 headers and 90 new elements ) and I was wondering how the thermocouples are normally attached and what type of NDE would be required for them ? It is my understanding that they are normally fillet/tack welded on to the tubes. I requirements in ASME Sec.1 in the PWHT section under P5A and it mentions capacitor discharge welding or electric resistance welding. I have never seen either of those processes performed before. Are there alternate NDE requirements / PWHT if you use SMAW or GTAW to weld them on ? It sounds like I need to get the design and location of these TC's from the engineer.





RE: Attaching Thermocouples to P5A Superheater Pendants
You have indicated pendants , which implies they are non-drainable. A good use for these T/C's is to confirm when all condensate has boiled out of the undrained inverts of the pendants during restarts. During initial firing you will see very high tube -to-tube temperature differences between the dry legs and the legs that are yet full of condensate. As soon as the temperature difference is less than 75 F then you can interpret that as final dry out of all legs and then you can increase the firing rate to higher values ( assuming all other permissives are met). As I recall , an old test at a Con-Ed boiler in 1961 indicated a 45 minute dryout period is typically needed at 10% heat input.
At normal load operations ( 30-100% MCR) you should record the temperature distribution of all of these outlet T/C's, to confirm the inlet orificing was correctly calculated and to confirm no tube is operating above is design metal temperature. If it is consistently a few tubes running hot then the header ligament region at those tube stubs would be the first header section to exhibit creep cracking.