CO detection in healthcare

CO detection in healthcare

CO detection in healthcare

(OP)
Our hospital has a direct vent fireplace. We have a plug-in CO Alarm (Kidde KN-COPP-3, plug-in with battery backup) in the same room as the fireplace. It's a single-station unit, so it doesn't report anywhere. NFPA 101, 2012 edition, Chap 19.5.2.3(2)(f) requires an "electrically supervised carbon monoxide detection... be provided in the room where the fireplace is located."

Does a plug-in style CO Alarm satisfy this requirement?

I think it doesn't. When i dive into NFPA 720, they distguish CO alarms from CO detectors.

I'm leaning toward having a detector tied into our fire alarm system, but report as a supervisory.

I will appreciate any feedback. Thanks.

RE: CO detection in healthcare

You haven't met that code with your plug-in device. Electrically supervised means that an alarm controller (like the fire alarm) monitors the device at all times and senses loss of connection. Here's a good place to learn more, and they also have the detectors you need. http://www.systemsensor.com/en-us/Pages/CO.aspx

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: CO detection in healthcare

If you install a supervised CO detector that is connected to a NEC Article 760 fire alarm circuit supervised by a Fire Alarm Control Unit, you will be in compliance with NFPA 720. If you are located in a jurisdiction that has adopted the 2012 International Fire Code, it contains retroactive provisions for the installation of either CO alarms or CO detection in existing Group I or R occupancies with fuel gas burning appliances.

RE: CO detection in healthcare

(OP)
Thanks everyone for confirming my gut. I have an electrician lined up to install one.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources