Storage of Contaminated/Used Fire Water
4

Storage of Contaminated/Used Fire Water

Storage of Contaminated/Used Fire Water

(OP)
Hello,

Could someone provide me some guidance on the following? I am trying to size a Oily Water Storage Tank (atmospheric pressure) to gather runoff of firewater in the event of a Oil Storage Tank rupture inside of a building. To clarify, if a Oil Storage Tank (Lube Oil) were to rupture and cause a fire, the fire protection system would activate. The runoff of this oily water needs to be collected in a tank and cant be drained to the environment. Does NFPA provide any guidance on sizing this tank? I am considering this oil-water mixture a flammable liquid (although the concentration is unknown), thus the storage of flammable liquid is why I am going to NFPA for sizing guidance.

I have seen something about it needs to be sized for 10 minutes of the Fire Protection flow. But would like a second opinion.

Thanks for your time,

RE: Storage of Contaminated/Used Fire Water

3
You may be able to find some sizing requirements in NFPA 30. If you're in a jurisdiction that's in the US that has adopted the International Fire Code, the requirements for containment are pretty clear which are:
    Volume of the largest tank or container +
    20 minutes of sprinkler flow calculated for either the area of the room or the design area of the system, whichever is smaller

RE: Storage of Contaminated/Used Fire Water

(OP)
Thank you very much Stookeyfpe!

I believe this is what I was looking for. Did some research and the state this is located in has fully adopted the IFC thus the IFC code should be used in place of the NFPA code. A co-worker has stated that in NFPA 850 there is wording that covers this topic for anyone else that needs a NFPA standpoint on this.

Thanks again,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources