Switch Rating
Switch Rating
(OP)
Our client asked that all switches be rated 8A@220VAC and 8A@24VDC., Our suppliers are struggling to meet the DC rating. the closest they can find is 10A@250VAC and 5A@30VDC. Am i right in thinking that this rating would be more than suitable?
Thanks
Thanks





RE: Switch Rating
RE: Switch Rating
RE: Switch Rating
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Switch Rating
Thanks
RE: Switch Rating
RE: Switch Rating
Make a note that not other devices may be operated through your interposing relays and/or that the end user must supply their own interposing relays for additional loads.
Letting an end user tell an OEM what must be used to operate their system is ridiculous and unwise.
RE: Switch Rating
However from a purely engineering standpoint if you are NOT using 24VDC, I don't see why that rating would matter to be quite honest. But if you are, and the LOAD on the switch might require it, then you are going to have to look harder.