Substation Double Fence Grounding

Substation Double Fence Grounding

Substation Double Fence Grounding

(OP)
Our substation has a security fence (encloses all substation equipment) and a separate perimeter fence (around the edge of the property line). Both fences are separately grounded with the security fence ground tied to the substation ground grid. I am using WinIGS to evaluate the touch and step potentials. Is it correct to include the perimeter fence in the computer model? This perimeter fence is installed in a concrete footing for its entire length and is about 20 feet away from the security fence.

RE: Substation Double Fence Grounding

The perimeter fence ground definitely needs to be included in the model. Modeling the fence concrete foundations can be modeled, but if left out will result in conservative touch-voltages.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources