Design of cooling coils in reservoir, close loop cooling

Design of cooling coils in reservoir, close loop cooling

Design of cooling coils in reservoir, close loop cooling

(OP)
Hello all,


Kindly point me in the right direction:

I'm hoping to design a low cost closed loop cooling circuit for our servo motors. I Would like to have tower/chiller water running through helical coiled tubing in my coolant reservoir tank to act as a heat exchanger. Since I dont know the all the inlet/outlet temperatures of coolant and water, how can I proceed to find LMTD in the heat exhanger equation to determine required heat exhange area? I estimated the peak heat load at 5700W.


Thanks in anticipation,
ABerlin

RE: Design of cooling coils in reservoir, close loop cooling

But, you should know your coolant flow rate; that fixes the Joule mass flow, which would determine your inlet temp. You need to then get your outlet temp down by the amount of heat originally added, so your outlet temp is determined. Now, all you need is your water flow rate, etc.

You know what your cooling tower does, so the problem is parametric with respect to water flow rate and cooling coil length.

TTFN
FAQ731-376: Eng-Tips.com Forum Policies

Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers

RE: Design of cooling coils in reservoir, close loop cooling

(OP)

Thanks IRstuff, that got me the T difference of the coolant and chilled water, I must be very rusty in thermo to have missed that.

What do you think about having a simple on/off solenoid valve on the water side for temperature control?

RE: Design of cooling coils in reservoir, close loop cooling

Better a throttle valve, and assume continuous (but variable) flow rather than on-off flow with the thermal mass of the pool being your control.

RE: Design of cooling coils in reservoir, close loop cooling

What are you going to do when/if the pool freezes over?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources