Secondary Containment Sump sizing

Secondary Containment Sump sizing

Secondary Containment Sump sizing

(OP)
Folks,

I've got a concrete secondary containment dike for a large tank. We've designed the low point location for sump placement. This sump will only be to provide an obvious low point for suction trucks to go to.

Is there a standard or rule of thumb for the sizing of the sump? 1% of the entire area? 0.25%?

RE: Secondary Containment Sump sizing

Big enough so that when the suction trucks are removing any spilled product the flow is continuous into the suction truck. If you size it too small, the flow into the sump won't keep up with the flow out.

RE: Secondary Containment Sump sizing

No, there is no standard size. Make it a practical size, maybe 3 ft by 3 ft.

RE: Secondary Containment Sump sizing

I would size it for a 25 year,24 hour storm as a guess, if the secondary containment is exposed to rainwater.

RE: Secondary Containment Sump sizing

If this is a RCRA (Hazardous Waste) Tank, the entire secondary containment system should be able to hold the volume of the largest tank plus the volume of the 25-year 24-hour storm event (Note: also address displacment of items in the secondary contatinment system). Most sumps I've seen are fairly small (e.g., 3' x 3' x 3') as they are only sized for small leaks/minor precipitation mainly to facilitate liquid removal as it's easier to remove liquids from a small depression than trying to remove a 1/4" of liquids over the entire containment pad.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources