Feedback for this CHS to CHS brace connections
Dear creators,
Please give your feedback for this CHS to CHS brace connections.
As the CHS member size and thickness are same, we developed CHS welded joints as discontinuous in both directions in order to avoid local failures in CHS member.
Please suggest any drawbacks on the proposed detail and looking ahead for your reply.
Thanking you
Arun S
Thanking you
Arun S
RE: Feedback for this CHS to CHS brace connections
If this has to be a welded connection, it is much better to continue one member through and weld the others to it.
I would prefer a bolted connection, with a plate split through the continuous member, and also split into the connecting braces. With heavily loaded compression members, it is sometimes necessary to then stiffen the connection laterally.
Michael.
"Science adjusts its views based on what's observed. Faith is the denial of observation so that belief can be preserved." ~ Tim Minchin
thank you for your guidance and your valuable time spend for me...
If you can't get the capacity required in the discontinuous member due to one of the limit states failing, I have in the past slotted an additional thick fin plate through the continuous member and used this to carry the loads (tension and compression) in addition to welding the 2 CBS together.