(OP)
I'm working on a revision to a dean's office at a local campus. The main air handler is a CV unit with no excess capacity. The new office layout will require additional cooling airflow than originally designed. What are my options to improve this situation? A fan-powered box would draw warm air from the plenum and probably not help with cooling. An inline booster fan may work, but would 'steal' supply air from other branches on the main duct. Any ideas on other options?

Thanks in advance.
Clymber

RE: Office - low airflow options

Ductless split system?

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Office - low airflow options

Fan coil unit mounted on wall?

RE: Office - low airflow options

try ductless systems

RE: Office - low airflow options

Take the existing air supply and see if you can design it into a displacement ventilation low level supply, and stratify some of the cooling load to the ceiling/return plenum. You can "effectively" get the cooling you need from low level displacement ventilation since a large percentage of the cooling load of the room is removed in the stratified ceiling air keeping the comfort level better at the human level of the room. May need to reheat or use that fan-powered VAV box to mix cooler supply air get the minimum temperature of the DV supply air up to +/- 63F-64F.

RE: Office - low airflow options

I likeGMcD thinking
The ductless suggestions are also good.
My additional two cents
You can re-sheave the CV fan for more airflow if your coil is sized for less than 500 fpm. You may be able to increase your CV system capacity, and rebalance the system. You can increase airflow thru the coil up to 500 fpm
My other three cents
You can lower SA temperature a couple of degrees or more (say from 55/56 to 53) and you may get enough capacity for your space, re-balance entire system of course.

RE: Office - low airflow options

- What is the percentage between new load and existing load?
- is there any load reduction in other parts of the building due to this renovation?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources