Mixing pipe.....

Mixing pipe.....

Mixing pipe.....

(OP)
I just came from a Building , in that building the contractor used a mix of galvanized and black pipe for an area. The system is a wet pipe system ordinary hazard(group 2). I have never seen the mix of regular black and galvanize pipe is this prohibit by the code. I was not able to find it in NFPA 13.

Regards
Lou

RE: Mixing pipe.....

Is this on a military base????

RE: Mixing pipe.....

Yeah..as long as the pipe is listed for fire protection use, then no problem.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

RE: Mixing pipe.....

(OP)
Is not an outside area, is an inside vehicle maintenance area with a wet system.

It is a military base. I know the newest UFC do not allow galvanize pipe at all. but this building was contracted few years ago.

RE: Mixing pipe.....

From a practical sense, why would you be concerned about galv pipe in a wet system?

RE: Mixing pipe.....

I would think if the entire pipe system is galvanized, not much of a concern, but the whole reason galvanized pipe is used is to protect from corrosion. If you have mixed pipes, and the galvanized pipe is the more predominant, then you will have water exposed to both zinc and the steel, which would quickly become a galvanic corrosion issue. If the galvanized pipe is the less predominant, then maybe it would be ok. The same rationale holds for installing small sections of copper pipe on steel sprinkler pipe, but never the other way.

RE: Mixing pipe.....

(OP)
SDpaddler50.

At this point I'm not really concern, the building was accepted like that by someone else. I have never seen that done anywhere else, that ‘s what pick my curiosity. I was thinking in the same line of what peddarin said. Is this a common practice?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources