External Static Pressure

External Static Pressure

External Static Pressure

(OP)

Hello

I need help in the following

1- A rule of thumb in calculating the external static pressure for supply and return air ducts

2- Web sites that have a detailed but easy to apply and user friendly methods in calculating external static pressure

I have tried the methods in ASHRAE and SMACNA and find then very lengthy, had to make too many assumptions, and hard to apply.

Thank you in advance

RE: External Static Pressure

You need to provide more information.  What type of application, ie, residence, institutional, commercial, anticipated velocity(if known), etc.  There are rules of thumb.  Just keep in mind rules of thumb are conservative, so an estimated static using rules of thumb should be higher than actual, meaning equipment will probably be oversized.  timr

RE: External Static Pressure

(OP)
Hello

the application is commercial building, the velocity is 1000 FPM, 1100 FPM, 1200 FPM.

By approximatly how much is it would be oversized?

RE: External Static Pressure

The practical limits for air velocity on humans are
between 1.5 meter/min and 10 meter /min
or 4.9 fpm -- 32.8 fpm.

Steven van Els
SAvanEls@cq-link.sr

RE: External Static Pressure

Approximately, in a commercial building, assume 0.1"/100ft. for the duct length entire. Then assume another 0.5" of the AHU PD. If the AHU has apecial filters then add the PD as per filters manufacturers. In a one floor office with supply and return ducting and diffusers I would estimate approximate 1.5" as the external static pressure. This needs to be checked later exactly as it could oversize the motor.

Hope the info was useful

RE: External Static Pressure

I also have a similar question regarding "External Static Pressure".   

 When viewing BLOWER DATA info, on for example, Trane XV80 gas furnace, External Static Pressure is always a factor on the chart, and is a fairly important one at that I'm sure.

  Where and at what point exactly to you insert probe in duct? Also, do you insert low probe in R/A duct at the same time as high probe in S/A duct? Is that .45 your ESP that you are seeing on you magnahelic guage?
  This exact manner in wich this measurment is performed has always been a big "?" for me, as it seems everybody has a differing view as to how it is correctly performed.

            PLEASE HELP!     Thanks, Rockhead

RE: External Static Pressure

Rockhead, Feb 10, 2001
I also have a similar question regarding "External Static Pressure".   

 When viewing BLOWER DATA info, on for example, Trane XV80 gas furnace, External Static Pressure is always a factor on the chart, and is a fairly important one at that I'm sure.

  Where and at what point exactly to you insert probe in duct? Also, do you insert low probe in R/A duct at the same time as high probe in S/A duct? Is that .45 your ESP that you are seeing on you magnahelic guage?
  This exact manner in wich this measurment is performed has always been a big "?" for me, as it seems everybody has a differing view as to how it is correctly performed.

            PLEASE HELP!     Thanks, Rockhead



 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources