Which VFD to avoid GFCI tripping?
Which VFD to avoid GFCI tripping?
(OP)
Hi,
I want to build an industrial sewing machine drive using a small VFD and a small AC motor. The AC motor will be a 4 pole 1400 rpm 0.25 kW induction motor and the VFD should be a 1ph 240V AC in and 3ph 240V AC out. There will also be a mechanical gearbox between the motor and the sewing machine to get the nominal speed in the correct range. The wire length from the VFD to the motor will be less than 1 foot. The wire length from the VFD to the 240V socket will be approx 10 feet.
I want to use my sewing machine at home where GFCIs are mandatory and I am worried that I will get tripping problems. Can anyone guide me in a direction in what VFD to buy ... or are ALL brands struggling with the GFCI problems? Or do I need to buy some extra equipment to make it work? Do I need to look for a particular VFD feature in the data sheets which eliminate the GFCI problem?
Thanks in advance
Lucas
I want to build an industrial sewing machine drive using a small VFD and a small AC motor. The AC motor will be a 4 pole 1400 rpm 0.25 kW induction motor and the VFD should be a 1ph 240V AC in and 3ph 240V AC out. There will also be a mechanical gearbox between the motor and the sewing machine to get the nominal speed in the correct range. The wire length from the VFD to the motor will be less than 1 foot. The wire length from the VFD to the 240V socket will be approx 10 feet.
I want to use my sewing machine at home where GFCIs are mandatory and I am worried that I will get tripping problems. Can anyone guide me in a direction in what VFD to buy ... or are ALL brands struggling with the GFCI problems? Or do I need to buy some extra equipment to make it work? Do I need to look for a particular VFD feature in the data sheets which eliminate the GFCI problem?
Thanks in advance
Lucas





RE: Which VFD to avoid GFCI tripping?
The text says that it can be used with 30 mA RCDs. That is true, but the text doesn't say that it also can be operated with 10 mA RCDs, which also is possible. In fact, the residual current in a typical installation is below 2 mA.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Which VFD to avoid GFCI tripping?
So what kind of sewing machine are you designing that will be plugged in and used in wet environments where a GFCI is going to be necessary?
"Will work for (the memory of) salami"
RE: Which VFD to avoid GFCI tripping?
That, I have measured, on a 400 V, 2,2 kW motor. The current was 0,7 mA RMS and that is without any filters and screened Cables. It is a fact and that is why DeLaval, the farm equipment producers, have selected this VFD for their milking and other machinery.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Which VFD to avoid GFCI tripping?
RE: Which VFD to avoid GFCI tripping?
As JRaef notes GFCI for ground fault protection are normally only found in wet environments (bathrooms, kitchens, outside, etc.), and not all over the home. Perhaps you're thinking of AFCI for arc fault protection? They have much broader use, but shouldn't interfere with a VFD.
Gunnar-
The NFO drives are interesting, but I have yet to find anyone offering them in North America. I'd love to try one out if they were available.
-Sean
RE: Which VFD to avoid GFCI tripping?
The Swedish inverter is highly interesting - however approx 10x more expensive than conventional ones - I got some prices from the Danish distributor.
I am happy to read that scottyUK does not have problems with his 30mA installation ... so maybe I should just go for a normal one.
Lucas
RE: Which VFD to avoid GFCI tripping?
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Which VFD to avoid GFCI tripping?
Using a drive on a domestic supply shouldn't just be viewed with the ( common) problem of tripping the breaker due to the leakage current. It should be viewed for protection. A fault on a device with a non-linear load ( eg a VFD) could a be a non-sinusoidal earth fault and not picked up by certain types of RCD(GFCI or HPFI). This means, the 'problem' would be that there could be a fault with a drive and the RCD does not trip.
The correct type of RCD should be used with a standard VFD. Unless of course, you use an nfo...
RE: Which VFD to avoid GFCI tripping?
2 picks from the list:
A 0,37 kW NFO costs the equivalent of approx 1600 Euros incl 25% Danish VAT (for end consumers).
A 15 kW NFO costs the equivalent of approx 5500 Euros incl 25% Danish VAT (for end consumers).
The abovementioned prices are without any rebates.
I am very sure that I can manage to find a 0,37 kW conventional VFD for 160 Euros incl 25% Danish VAT.
Lucas
RE: Which VFD to avoid GFCI tripping?
RE: Which VFD to avoid GFCI tripping?
Thus the pricing Lucas obtained for NFO appears to be about 10x higher than conventional VFD's. This could help explain why NFO drives aren't more prevalent and available, given their other advantages. I still hope they enter the North American market so I can try them out someday.
-Sean
RE: Which VFD to avoid GFCI tripping?
http://www.delaval.com/en/-/Product-Information1/M...
I looked into them a few years back (at Gunnar's suggestion), the problem they have for our marketplace is that they stop at 400V class and range up to 440V +10%, but that's not adequate for the real world of US 480V nominal systems, which frequently climb to 500+. So here in the US, they would only be able to be used in 230V applications, and that market is saturated with VERY cheap drives from Asia.