For which type of valves fire safe test is mandatory? and What is its standard? API 607 or 6FA?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: fire safe
API 607 4th ed. is not generally accepted for soft seated valves up to class 600 since both the operational and external leakage tests are carried out at only 2 bar compared to other procedures.
In addition to that, local (Plant / country) best practice might also be applied. For instance during the first XX minutes, shall there is leakage through (damaged) seal or joints it Should not provide significant contribution to the pool of fire or Blast in the pipeline. Or better, NO leak at all.
Period for offshore platform normally 15 minutes (zero leakage or acceptable external leakage as per ISO 10497). This period is considered as a maximum time required for all personnel to evacuate from platform (into that small ship and launched).
For refinery or Onshore normally 60 minutes (acceptable external leakage as per standard). This is the time required for Fire fighter to extinguish small fire (starting from the alarm ringing) and not the pool of fire.
I am not quite sure whether the material selection for this type of valve is also governed by such standards. Other constructive inputs are highly appreciated.
Regards,
MR
RE: fire safe
Biggest issue with API 6FA is the valve size qualification range. ISO 10497 allows vendor to fire test an 8" valve to qualify all sizes larger while API 6FA does not allow vendor to do so.