Am I correct in thinking that if a rcd feeds a transformer, then anything connected to the secondary of the transformer will not be protected by the rcd and another rcd is required to provide protection
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: RCD protection
But only if it is an autotransformer (no isolation between primary and secondary).
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: RCD protection
An rcd on the primary of a normal transformer ie two electrically isolated coils would not provide protection to the circuits on the secondary
is that correct
RE: RCD protection
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: RCD protection
Did you mean to say "Unless" rather than "But only if" ??
On the other hand I'm still on my first cup of coffee this morning.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: RCD protection
Of course it should be "unless". I think that richerdick got it. And that was NOT exactly what I said.