Snipping Strands of Stranded Conductors

Snipping Strands of Stranded Conductors

Snipping Strands of Stranded Conductors

(OP)
I have always thought that the Code (CEC and/or NEC) inhibited the snipping off of some strands of conductors - say for example - to make a larger conductor fit into a smaller lug. I thought that the correct way to do it would be to crimp on a reducer (for example if you use #10 or #8 for voltage drop to an outlet that has terminals for #12).

However, I can not find a specific code item for this. Perhaps it is just good practice?

RE: Snipping Strands of Stranded Conductors

The lug will be listed for use with certain conductor sizes and will have instructions for use. Anything outside of that means the lug is not correctly applied and is a code violation. And stupid.

RE: Snipping Strands of Stranded Conductors

DPC is right. You won't find a specific code reference for snipping strands. Following manufacturers' instructions is implied.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Snipping Strands of Stranded Conductors

Actually, it is in there. 110.14 (A)

Quote:

Terminals. Connection of conductors to terminal parts
shall ensure a thoroughly good connection without damaging
the conductors...

"Will work for (the memory of) salami"

RE: Snipping Strands of Stranded Conductors

I can hear it now - "I cut off the strands so they wouldn't get damaged." cheers

There is also 110.12 - "Electrical Equipment shall be installed in a neat and workmanlike manner."

Our specs generally reference NECA standards as well.

RE: Snipping Strands of Stranded Conductors

(OP)
Thank you all. Same page (I rejected install).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources