beam deflection L/360
thread507-37706: Allowable Beam Deflection
Hello Everybody after reading the reference thread i just want to figure out the meaning of 360 on the deflection parameter, where this number came from? it has any units? if my deflection calculations are in metric units i use the same value? what are the conditions to compare this parameters... i undestand that in imperial system the value of L must be in inches, what about in metric?
thanks a lot for any comments.
RE: beam deflection L/360
Some of the other deflection limits are also set by the type of finish applied to the member. Brittle finishes need tighter deflection limits to prevent cracking etc.
All it means is that you are limiting the vertical deflection to 1/360th of the span of the beam, a common limitation for sheetrock and plaster ceilings to limit cracking of the joints.
Mike McCann
MMC Engineering
Recently, a senior colleague told me that he feels that L/XXX is intended to limit the maximum slope occurring along a member for occupant comfort. I'm not sure that I buy it but it's a novel take on it.
At roofs, of course, there is ponding to consider.
When I've been aggressive with deflection limits, I sometimes wonder about the impact of movement on my connections. Is a single plate shear tab still a moment free thing with end rotations commensurate with, say, L/90 deflection? I'm not sure.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
If you are working to a specific figure, you need to establish whether it is just under imposed load, or imposed plus dead load
It is probably more rate of change in slope that is being limited, so curvature as you first suggested.
Some of us in metric countries have adopted L/250 and L/500...
... but it will resonate around 4Hz, which they will describe as 'a little bouncy' when they dance on it.
Mike Halloran
Pembroke Pines, FL, USA
Yep, I always assumed the same. With the span measured in feet and the deflection measured in inches L/360, 240, 180 become L/30, 20, 15 respectively.
It's similar to the reason concrete compressive strength is measured at 28 days: that's divisible by 7 so the testing cylinder break won't have to occur over a weekend.
Keep in mind these are minimum and there are many reasons to have stricter deflection limitations.
"Look for 3 things in a person intelligence, energy and integrity. If they don't have the last one, don't even bother with the first 2. W. Buffet