Capacity of Underground fire fighting RCC tank

Capacity of Underground fire fighting RCC tank

Capacity of Underground fire fighting RCC tank

(OP)
I need the capacity of a fire fighting tank for 13 nos. external fire hydrant outlets. The selected pump size for the project is 500 GPM. Please advice me for the capacity of Underground fire fighting RCC tank as required to British standards.

RE: Capacity of Underground fire fighting RCC tank

Not an engineer or near it

But what are you going to protect with 500 gpm a Waterloo?
 

RE: Capacity of Underground fire fighting RCC tank

I would contact the local fire marshal or insurance company. The number of fire hydrants to be used at the same time and the amount of time required for the water supply to last will depend on the type of businesses and occupancies for which this water supply is to be dedicated during a fire.

RE: Capacity of Underground fire fighting RCC tank

Dear it seems your fire pump capacity is taken considering 2 fire hydrants open at a time. Usually all codes and standards requires 250 gpm per hydrant. As you interested in the fire tank capacity, you must check that this tank is gonna supply only to your hydrants or there are other fire fighting means are also available in the project. If you have only fire hydrants, then you need to check prevailing code/ AHJ of your area and their minimum requirements. Usually they ask for 2 hours but also need to look at your hazard type. If its normal light or ordinary hazard as per NFPA you can consider your duration for 2 hours. In that case your fire tank will be of 500*120*3.785/1000=227.1 Cubic meter. You may also add a suitable safety factor from 10-25%.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources