We have a Weg Motor data sheet that says the voltage is
380-400-415/660-690v 50hz
Motor is 110kw
The clients supply is 400v and motor rated voltage is 400v
So if we connect it in delta we should be fine for 400V?
Thanks
380-400-415/660-690v 50hz
Motor is 110kw
The clients supply is 400v and motor rated voltage is 400v
So if we connect it in delta we should be fine for 400V?
Thanks





RE: Multi voltage motors
The windings have enough copper to safely carry the heavier current when developing rated power at 380 Volts. There is enough iron to take 415 Volts without saturating. When the windings are connected in star on 693 Volts each winding will still receive 400 Volts.
Connect the motor in delta for 400 Volts.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Multi voltage motors
Just to be sure I've got this 100% correct, the clients spec says that their power supply is 400v 50 hz and their motor rated voltage is to be 400v.
So if we connect this weg motor(110kw)in delta it will be fine for the application?
Another concern I have is that what if someone tries to connect it in star?
Thanks again
RE: Multi voltage motors
Specifically:
Connected Wye, the voltage across each coil is 400/sqrt(3). Motor torque portional to E^2. Speed is portional to frequency. So, the speed-torques curve shape doesn't change, just drops (not exactly true - but should be close enough for this example)
So, motor power drops to ((400/sqrt(3))^2)/(400^2) ----> say to 1/3 of nameplate. You would have a excellent, robust, cool running, 37kW motor, running at the same speed and slip as if it were connected delta across 400V.
ice
Harmless flakes working together can unleash an avalanche of destruction
RE: Multi voltage motors
RE: Multi voltage motors
So yes, you will want to connect that motor in Delta if you are going to run it on 400V. DO NOT connect it in Star.
"Will work for (the memory of) salami"
RE: Multi voltage motors
I sense a slip of the fingers there.
400 is 690 / the sq. rt. of 3
works better, or swap the 400 and the 690 in the original.
RE: Multi voltage motors
Actually, I did it extemporaneously then checked it as 690 x .58 because the division key on my ancient desk calculator is stuck! I just screwed up what I called it... because it technically should have said "400 is 690 x the inverse of the sq. rt. of 3", which just sounds stupid. So I fixed it in terms of the verbal description but forgot to swap the places on the values when I changed back from using the inverse... <slaps head>
"Will work for (the memory of) salami"
RE: Multi voltage motors