Slab on grade reinforcing

Slab on grade reinforcing

Slab on grade reinforcing

(OP)
What is the minimum reinforcing required in a slab on grade or ground for shrinkage/temperature cracking?

RE: Slab on grade reinforcing

From ACI 360R

Assuming regular slab-on-grade, no prestressing etc.

As = (F*L*w)/(2*fs)

As = Area of reinforcement (sq. in.) per foot width of slab
F = Friction Factor (dependent on base and subbase - "typical" is 1.5)
L = Distance between joints (ft)
w = Dead weight of slab (psf)
fs = Allowable stress in the rebar (psi)

Might want to consider factors such as loads, application etc. to tweak this as necessary.

RE: Slab on grade reinforcing

For a non-structural slab on grade- Zero would be the minimum. Just space your joints properly.
Un-reinforced slabs are very common for residential and office type applications. Wouldn't recommend it for industrial or warehouse


RE: Slab on grade reinforcing

Also have to consider ACI 350-06 and hazardous materials or chemicals containment constraints, substantially increasing the minimum reinforcing..

Mike McCann
MMC Engineering

RE: Slab on grade reinforcing

ACI 360 "Guide to the Design of Slabs on Ground" is the reference you need! Generally it is most economical to obtain the necessary strength by increasing the thickness of a plain slab than it is to reinforce for strength. As far as T&S, control joints at the correct spacing, is the most economical solution. If you can use control joints, then the new recommendations range from .15% to .5% of the gross area of concrete . The formula jreit refers to is the old Subgrade Drag Theory. It has been removed from the new ACI 360.

RE: Slab on grade reinforcing

We did many warehouse/commercial buildings with un-reniforced slabs. Proper sub grade prep and concrete mix and placement/saw cuts was critical, but many are still uncracked toay. Mesh/rebar for a 100K sf warehouse is expensive, and generally does not help, since it isnt in the slab correctly usually.

RE: Slab on grade reinforcing

If you CAN'T use control joints...

I should have taken typing in high school! My mind is way faster than my two fingers!

RE: Slab on grade reinforcing

Splitrings, I wasn't aware that the code had changed. Thanks for clearing that up.
Any idea why they removed it?

RE: Slab on grade reinforcing

The subgrade drag equation was not included in ACI 360-06. I didn't catch it until I just got ACI 360-10. The only guidance in -10 is the recommendation of .5% reinforcement to eliminate control joints. ACI 350-06 has a table based on joint spacing but this reference is for environmental structures. It also has the same upper percentage of 0.5% in joints are not used. I haven't seen any commentary explaining why it was removed.

RE: Slab on grade reinforcing

Hello, I'm practicing in Europe, and I have a question about foundation slab design. Let's say we have a slab 20 x 30 meters, 300 mm thick, and designed with top and bottom mesh to resist building loads (let's say steel or wood). Commonly we don't specify any joints or sawcuts. And it works. Small cracks form but are not an issue. I want to understand american practice with many control joints and sawcuts I'm reading about.
ACI states you need to use .5% reinforcement if there are no joints - for the example slab that would be 15 cm^2 of reinforcement (sum of top and bottom?) which quite a lot. Most of the designs don't have such an amount of reinforcement.
In my area contractors deal with crack control by dividing slab with more pours, using special concrete mixes, even pouring slab in two layers and adding micro reinforcement.
I would love to read about your experience.

Kind regards

Structural timber engineering

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources