what the sizing pipe of side wall sprinkler k-factor 8 ?!!!
please advice,
please advice,
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: k-factor 8 pipe sizing
Travis Mack
MFP Design, LLC
www.mfpdesign.com
RE: k-factor 8 pipe sizing
You need to first specify your hazard type, its light/ordinary or extra ordinary... after that you can do it in two ways;
1) You can use the normal schedule pipe sizing of NFPA 13 for given hazard and perform a hydraulic calculation and look on the pipe velocities and your required pressure at pump discharge. If they are in acceptable limit you can be ok with schedule sizing. otherwise start increasing the size from last node to suit the pipe velocity limits.
2) Another thing you can do is start from hydraulic calculation and confirm your sizes.
RE: k-factor 8 pipe sizing
then do hydraulic calculation & pipe sizing by keeping velocity and friction factor within limit.
the pipe schedule method is applicable to most of application but most suite to K-5.6 or nearest values.
for higher K value , off course flow would be higher than K-5.6
and consequently pipe size.