Hello,
I've had a ground fault in my system for which an event recorder (SR750) is giving me ground currents that are not possible. This is a 6900V delta system with a 400A (10ohm) neutral grounding resistor. The phase and ground currents shown from the recorder are as follows:
A = 2810A
B = 3216A
C = 6854A
G = 1265A

I know that mathematically, the zero sequence current is 1285.69A. However, the maximum current possibly flowing through ground is 400A, as set by the NGR.
Has anyone run into this scenario before? I am assuming it is just a measurement anomaly, but unsure as to what is causing it, whether it be the CTs, the AC signal filters, the firmware, etc.

Any insight would be greatly appreciated.

Thank you.

RE: Incorrect Ground Current Measurement

I may be out on too deep waters here. But how can you have a Neutral in a delta system? Where is the 10 ohm resistor connected?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Incorrect Ground Current Measurement

Unless you have a CT from the neutral going to the relay, the "G" value is probably just the phasor sum of the three phase currents. This had to involve more than a ground fault since your C phase was over 6800 A.

I haven't fiddled with an SR750 or its event reports for quite a while. If you have waveform capture, that might be more revealing. Otherwise, you may need to resort to looking at the relay manual or talking with Multilin. I would not assume there is a relay error until you know how the "G" value is determined and eliminate the other possibilities. Relay error is probably the least likely problem.

RE: Incorrect Ground Current Measurement

(OP)
Sorry my mistake, the main sub transformer is delta/wye with a 10ohm NGR. There are no single phase loads.

RE: Incorrect Ground Current Measurement

(OP)
There is a core balance CT going into the SR750 relay (no CTs on the NGR are used in this relay). Yes, dpc, the fault progressed into LLG at some point.

RE: Incorrect Ground Current Measurement

To calculate I0 you apparently assumed 120 degree angular displacement. Why would you assume balanced phase angles when magnitudes are unbalanced? Where does one attach an NGR to a delta system?

RE: Incorrect Ground Current Measurement

(OP)
Thanks for the responses. Yes, it is probably incorrect to assume balanced angles in an unbalanced fault. However, it seems that the relay has made the same mistake?
I am just curious if anyone has ran across this issue before.

RE: Incorrect Ground Current Measurement

I'm still not convinced the "G" represents the flux summation CT current. I'd do some additional research as to the meaning of the "G" current.

RE: Incorrect Ground Current Measurement

ZeroSeq,
If the secondary of the Dyn transformer is connected with a 400A rated NGR, then there is no way that during a ground fault the max allowable ground fault current is greater than
400A. The ground fault current = 3 x zero seq current. Therefore, it looks like there is multiplication factor issue.

RE: Incorrect Ground Current Measurement

If the SR750 is not correctly computing the ground fault current, I have to believe that GE/Multilin must be aware of this. I would send your fault data to them and ask them to explain. Perhaps your relay needs a firmware upgrade.

RE: Incorrect Ground Current Measurement

Check the CT wiring. Under normal load, does the SR750 metering show correct phase angles?

RE: Incorrect Ground Current Measurement

(OP)
Thanks for all the suggestions. I am in contact with Multilin, and will update with the response I receive.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources