IEEE 242 - Cable Overload Time-Current Curve Data Points

IEEE 242 - Cable Overload Time-Current Curve Data Points

IEEE 242 - Cable Overload Time-Current Curve Data Points

(OP)
I'm working on a project to determine Solid State Trip Controller S/L/I settings for Low Voltage, 480V Circuit Breakers for both feeder and branch circuits. In order to do this, I've been plotting motor thermal damage curves on the Controller Time-Current Curves to select approrpiate LTPU and delay settings. I'm currently at the point where I'm trying to plot thermal damage curves of cable in accordance with IEEE 242-2001 Reccommended Practice for Protection and Coordination of Industrial and Commerical Power Systems, Section 9.5 - Overload Protection of Cables. Within this section, IEEE utilizes the following equation to develop a table for cable overloads:

Perecent Overload Capability = Ie/In % = SQRT(((Te-To)/(Tn-To)-e^(-theta*K))/(1-e^(-theta*K))*(230+Tn)/(230+Te)*100)

where: Te = Conductor Emergency Temp
Tn = Normal Temp
To = Ambient Temp
K is a constant, dependent on cable size and installation type (See Table 9-5)
e is base for natural logs

This equation is used to develop the table in 9-6:
K = 1, Insul - THW, Tn=75C, Te=95C

Time % Overload
10s 987
100s 329
1000s 148
10000s 121
18000s 121

I can not figure out how they tabulated this data from the aforementioned equation. I believe there is an issue with my Time Constant Value "K" in the equation. I'm not sure what theta is and how to express the K Value in this equation to get the values they get in their tables.

RE: IEEE 242 - Cable Overload Time-Current Curve Data Points

There are some mistakes in your formula:
1)If it is in excel [Microsoft] it is better to put exp() instead of e^().
2)the last digits [100] have to be out of radical:
Ie/In% = SQRT(((Te-To)/(Tn-To)-exp(-Θ*K))/(1-exp(-θ*K))*(230+Tn)/(230+Te))*100bigsmile

RE: IEEE 242 - Cable Overload Time-Current Curve Data Points

I almost forgot it: Q[theta] =duration of overload in hours=secs/3600

RE: IEEE 242 - Cable Overload Time-Current Curve Data Points

(OP)
1) Yes I was using exp - thank you

2) After playing around for another 2 hrs, I finally realized it was out of the radical hahah. Such a simple mistake took me 2 hrs to figure out.....

3) I did finally realize it was in hours instead of seconds. It would be nice if IEEE posted units in their variables...

THANK YOU for the quick response!!!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources