Calculate electric bars
Is there any body can tell me where can I find information about electric and mechanical efforts in the electric bars of a transformation center. I found some information of SF6 but I need more about other ways of isolating and even if there are programs or equations to set the layout of the bars and overcome the mechanical efforts of the electrical faults.
It´s to get some information for my end of career project so I'd thank any recommendation to bibliography or web.
RE: Calculate electric bars
There are several great references on the mechanical effects on bus structures due to short circuit currents. These references are:
-C. H. Van Asperen, AIEE Toronto Section Meeting of November 5, 1922, "Mechanical Forces on Busbars Under Short-Circuit Conditions" This paper was awarded the "First Paper Prize" for the year ,1922, by the AIEE. The paper is technical in nature and also discusses the predictions of theory with labortory  tests.
-Stanley C. Killian, Development and Research Engineer, Delta-Star Company. Electrical World Dec 12, 1942, "Mechanical Forces on Buses Due to Fault Currents"
-H. B. Dwight,Electrical World, Vol 70, September 15, 1917 page 522 "Repulsion Between Strap Conductors"
-C. W. Frick, GE Review, Vol 36, May 1933, page 232, "Electromagnetic Forces on Conductors With Bends, Short Lengths and Crossovers"
--H. B. Dwight, AIEE, presented at 36th  Annual Convention, June 20, 1920, "Calculation of Magnetic Force on Disconnecting Switches"
-H. K. Porter Company, Inc., Bulletin 38-E, Section 1, Power Conductors-Technical Data Section. This bulleting contains references to many articles by S.C. Killian of Delta-Star Company.
-ITE Circuit Breaker Company, Bulletin No.2603-2A, "Electrical Buses and Bus Structures" by William Deans, Copyright 1959.This 47 page bulletin is probably the most comprehensive summary of the the preceeding references. This publication presents several nomograms useful for bus design and I find it most useful when evaluating the existing  short circuit bracing on bus structures.
-Book by ALCOA, Alcoa Aluminum Bus Conductor Handbook,Copyright 1957. Chapter 6 "Short-Circuit Conditions" covers this topic and lists other references, some of those mention above and others.
Suggestions: Try to see practical aspects over manufacturers and industry standards too:
1. Go to
http://www.thomasregister.com
find companies which manufacture buses, e.g. Siemens, Cutler Hammer, Westinghouse, Busway Systems, etc. and ask them for engineering/design literature which is usually helpful for applications.
2. Try libraries for literature, e.g.
2a. Standard Handbook for Electrical Engineers
2b. IEEE Standards 141, 241, 242, 605, C37.20.1, C37.20.2, C37.20.3, etc.
2c. NEMA Standard BU1
2d. ANSI/UL Standard 857