Storage Rack Braceing

Storage Rack Braceing

Storage Rack Braceing

(OP)
Is there a specific requirement for bracing of storage racks based on seismic design categories, similar to anchorage of mechanical equipment? I'm thinking in specific SDC, bracing is not required and in higher SDC it is. I've skimmed through the RMI but it looks like that is more for the design of the racks, not for bracing based on SDC.

RE: Storage Rack Braceing

ASCE 7-10 1.4.3 under General Structure Integrity, requires that all structures be analyzed for lateral effects regardless of SDC. The Design force = 1% of the structures dead load.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources