I couldnot exactly remember which BS standard,but it mentions maximum incomer isolator possible for a distribution board is 125A.Whether
such a rule exists-When I look to well known manufacturers productline,I can see it exists.

My question is on what basis such a rule is made?

choice 1 -->considering arcing factor,means form of construction??

choice 2 -->considering 10A is the minimum mcb fits into at outgoing.So to provide a safety at upstream on short circuit conditions??If more than 125A used, it maynot
be possible to take control by discrimination laws.

I would be grateful if somebody can shed light on this.

tHANKS IN ADVANCE

ABRAHAM

RE: FINAL DISTRIBUTION BOARD ISOLATOR RATING

Most of your assumptions are untrue.

Arguably the most common range of industrial DBs in the UK - the Schneider Isobar 4 series - has main bars rated for 250A. Outgoing MCBs are available down to 2A, although they're not especially common at such a low size. The Multi 9 MCB on its own is good for 10kA, but when backed up by an MCCB as the incomer to the board the MCB is capable of operation at 25kA fault level.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources