Hi All,
In concrete design, does the allowable span depth ratio ensures that vibrations due to live load will not affect occupants? say for example I have 12' (3.75m)span continuous slab with a residential live load of 42psf (2kPa), if I use of 6" (150mm) thk slab would i feel significant vibration if people at the next room are running, jumping or doing some sort of activity?
I know that the span depth ratio is there to control excessive deflection. I dont know if applying the span depth ratio would also take care of the vibration problems, and the code has no guideliness on how to control vibrations.
In concrete design, does the allowable span depth ratio ensures that vibrations due to live load will not affect occupants? say for example I have 12' (3.75m)span continuous slab with a residential live load of 42psf (2kPa), if I use of 6" (150mm) thk slab would i feel significant vibration if people at the next room are running, jumping or doing some sort of activity?
I know that the span depth ratio is there to control excessive deflection. I dont know if applying the span depth ratio would also take care of the vibration problems, and the code has no guideliness on how to control vibrations.






RE: Slab vibration
The allowable span to depth ratio does not ensure acceptable vibration response. But I don't think you will have vibration issued for the span you dealing with.
RE: Slab vibration
if you are ever worried about vibration however there is a very simple hand check you can do to determine the natural frequency of the floor structure, which is a function of the dead load deflection - see the attached extract with the formula. You basically work out the natural frequency and if it is greater than 4.5 Hz vibration should not be an issue.
RE: Slab vibration
RE: Slab vibration
RE: Slab vibration
RE: Slab vibration
4.5Hz is very close to the second harmonic walking frequency and the structure will be susceptible to both impulsive and resonance response. The vibration could be unacceptable if the peak acceleration is >0.75%g. See attached figure from AISC.
RE: Slab vibration
Thank you for the reference vibration calculation.
RE: Slab vibration
It came to my attention again one day when I was messing with an assembly driving by a small stepping motor (nothing nominally unbalanced, just commercial components), and decided to slowly sweep it up from 1Hz to 1000Hz to test the electronics.
... on a heavy table in my second floor lab.
As the machine swept through 3 to 4 Hz, the entire population of the machine shop downstairs came running up to see how the hell I was shaking their ceiling so badly.
I had to run the sweep again in their presence, after they had searched the lab and not found some kind of seismic death ray machine, to show them how little energy it takes to excite a resonance.
After that I programmed the machine to just start above 20Hz.