Hello All,

New to this forum, but I have a question about the clear spacing between bars. For the purposes of calculating development length, ACI318-11 12.2.2 allows you to use the reduced value if the clear spacing between bars is at least twice the bar diameter. Does this spacing restriction apply in the vertical direction between layers as well as in the horizontal direction?

It seems like it would based on the language of the commentary and table, but the commentary makes specific reference to 7.6.1 (the section on horizontal clear spacing) without mentioning 7.6.2 (the section on vertical spacing). Thanks.

Jeff

RE: Clear Spacing between rebar layers

The clear distance is for two principle purposes: 1) to assure that good consolidation around the bars is possible, and 2) to be sure there is sufficient concrete around bars to provide confinement using the tension capacity of the concrete. In this case you mention, I would not be concerned about having sufficient confining concrete, but would be concerned about reduced consolidation. Where bars are too close together, you can end of with only concrete paste between bars (uneven distribution of large aggregate) with the end result of easier tension cracking along the bars and potential for shrinkage cracks as the paste cures and shrinks.

RE: Clear Spacing between rebar layers

1 1/2 times the larger aggregate

RE: Clear Spacing between rebar layers

As given in ACI 117 (Tolerances)....

2.2.4 Distance between reinforcement:
One-quarter specified distance not to exceed
. . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 1 in.
Providing that distance between reinforcement shall not be less than the greater of the bar diameter or 1 in. for unbundled bars.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close