Guardrail Loads in 2009 IRC

Guardrail Loads in 2009 IRC

Guardrail Loads in 2009 IRC

(OP)
I would swear it is in there. Does anyone know where the design load is specified for a Guardrail in the 2009 IBC? R312 doesn't specify a load. I believe it is 200# regardless of post spacing, which is less stringent than the IBC requirement.

RE: Guardrail Loads in 2009 IRC

Section 1607.7.

RE: Guardrail Loads in 2009 IRC

(OP)
JStephen,

That is the IBC reference. I need the IRC reference.

RE: Guardrail Loads in 2009 IRC

Sorry, I was reading the text and not the title.

RE: Guardrail Loads in 2009 IRC

(OP)
No worries, I fully expected the IBC reference to appear. :)

RE: Guardrail Loads in 2009 IRC

just read the sections in the IRC, and I couldn't find anything about load :\.

RE: Guardrail Loads in 2009 IRC

If you want to backwards-engineer it you could check out the AWC's proscriptive requirements for wood decks found here:

http://www.awc.org/Publications/DCA/DCA6/DCA6-09.p...

See pages 15 & 16.

I found it noteworthy that they had modified their joist spans for Southern Yellow Pine, presumably because the design values for that species was downgraded recently.

RE: Guardrail Loads in 2009 IRC

(OP)
Thanks Archie263. 199 pounds it works out to. I will be generous and round up to 200#. I would swear it is somewhere in that disaster that is the IRC, just can't find it.

RE: Guardrail Loads in 2009 IRC

dcarr....the residential code is a subset of the building code, therefore covering only those items unique to residential. Guardrails are not unique and therefore covered under the building code. See Chapter 1 of both codes for applicability.

RE: Guardrail Loads in 2009 IRC

Table R301.5 in IRC-2012. 200 lbs concentrated load on guardrails and handrails. No requirement for 50 plf

“Faith is taking the first step even when you don’t see the whole staircase.” MLK

RE: Guardrail Loads in 2009 IRC

(OP)
Thanks Bagman.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources