Can anyone give me some tips about grounding high voltage cables for substations? There is an existing substation and ground, but it will undergo construction because the building is dilapidated. I'd just like some input on how to ground high voltage cables ( 13.2 kV). Thanks






RE: High Voltage grounding for substations
a)cable shield-if the cable remains in operation.
b)single conductor at both ends-in order to avoid induced voltage build-up from adjacent cables in operation.
c)both conductor and the shield for the same reason as in point b.
RE: High Voltage grounding for substations
Option C. Also the HV cables are for 34.5 kV and not 13.2 kV. Thanks!