I have MV breakers in series: Main breaker to a Feeder breaker – Feeds another gear with a main and feeder breaker. I am wondering the minimum time that should be allowed for coordination. I think IEEE recommends 4ms but I think that was based on the old electromechanical relays, is 1ms sufficient? I have heard but not seen white papers recommending 2ms.
Thank you.
Thank you.






RE: Electronic Relay Protection
With digital relay coordinating with digital relay, I'm very comfortable with 0.25 seconds, and have been known to go down to 0.2 seconds without losing much sleep. It will take a digital relay much longer than 1 ms to even figure out that a fault has occurred.