Retrofit high service pumps with VFD
Hello Everyone,
We are installing VFDs on our High Service Pump Station pumps at the WTP. There are currently 3 large (duty pt.:6,000 gpm @ 360' TDH)and 2 small(3,000 gpm @ 360' TDH) constant speed split case centrifugal pumps. The pumps have been running out on the curve causing excessive maintenance and repairs due to cavitation. Therefore VFDs are being installed to run the pumps closer to the BEP, reducing costly repairs and energy costs. VFD will be initially installed on 2 large pumps and 1 small pump. I need to develop a functional description for operating these pumps. This project was developed by another engineer at our water system who has since left and the VFD installation is almost complete so there are no other options to consider for the original problem(like impeller trimming or control valves).
WTP staff prefers to operate the pumps based on elevated storage tank levels versus pressure or flow. I am going along with this for now. With varying demands, typical scenarios will be one small pump running, one large pump running, one large and one small pump running, and possibly two large pumps running. All these scenarios will have pumps running at less than full speed (still need to work this out, though). The tricky part is running a small and large pump together in parallel(could have the large pump on VFD and one small constant speed pump combination). I see almost endless combinations. Any suggestions on speed control using tank levels and how to approach the varying pump combinations.
Thanks in advance.
RE: Retrofit high service pumps with VFD
So you have some kind of analog level signal for the tanks? Are you filling more than one tank at a time off a common header? Level control should be much simpler than pressure or flow control, but you'll have to decide which level signal you are controlling with. So you don't need a pump running to maintain system pressure? You can probably run both the large and small pumps from the same level signal.
DO you have any flow information? Separate flow info?
Keith Cress
I would consider setting the pumps at a safe constant speed or at the most efficient speed and let the operators control them as they wish.
It is a little kludgy but you could use three or four level switches. Instal a selector switch for each motor so that the operators may select either level 1, 2, 3, or 4 to control each pump. The operators will love it. More than one pump may be controlled by each level switch depending on the selections.
You could also use level transmitters to bring the pumps online and control the speed over a small range.
We could design a fairly simple system with a combination of level controls controlling the pump speeds over a small range and level switches to bring more pumps online as needed.
A PLC may be able to handle it all with just a level transmitter input.
Bill
"Why not the best?"
Jimmy Carter
I think you have an excellent point Bill. Manually run them to the points desired. Once they're understood set up a simple PLC to control all the desired steady-states.
Keith Cress
Do they really need to control level? Using on-off control and running the pumps at BEP will use the least amount of electricity.
The more time I spend and more people I talk to the more I'm of the belief that VFD's are useful for process control only. There is always a better option if you want to save energy compared to using a VFD.