B31.1 NDE Requirements
I am working on a piping specification for B31.1 (2012) boiler external pipework and I am trying to check the NDE requirements according to the code. The only reference I can find is in section 136.2.1 where it states "....For specific requirements see the applicable parts of Section 1 of the ASME Boiler and Pressure Vessel Code, PG-104 through PG-113....". When I look in the Pressure Vessel Code there are no sections PG-104 through PG-113 and pages 104 through 113 deal with pressure relief and part of methods of fabrication but does not include any NDE requirements.
I have three questions:
Am I missing something in the B31.1 code?
What is the B31.1 Code referring to?
Should I just use the relevant parts of the Pressure Vessel Code?
RE: B31.1 NDE Requirements
NDE requirements are clearly listed in Table 136.4 of B31.1.
JM, I think you might be missing something.
The B31.1 Code is refering to Section I of the BPVC -- did you perchance look in Section VIII, Division I? When I went to Section I, I found PG-104 to 113 and they dealt with certification marks and stamping just as B31.1 136.2.1 discusses. But as Weldstan says, go look at b31.1 136.4 for NDE requirements.
Want to know the do's and don'ts of Eng-Tips? Read FAQ731-376: Eng-Tips.com Forum Policies.
English not your native language? Looking for some help in getting your question across to others or understanding their answers? Go to forum1529: Translation Assistance for Engineers.
Yes, I completely missed that table and yes, I was looking at Division VIII.
Thanks for your help!