Tubular Airheater Design

Tubular Airheater Design

Tubular Airheater Design

(OP)
We are repairing a tubular airheater in a stoker coal fired power boiler. Expected exhaust gas temperature at under 450 deg. F. Scheduling has forced us to look at available practical material options. What is the effect of a change from 2" OD x.083"T to 2" OD x .095"T on operation? Is ASTM A 513T (1010) a suitable material?

RE: Tubular Airheater Design

Materials selection may be more affected by fuel type with specific chemical composition as well as effects of boiler loads. Cold end corossion will quickly degrade common carbon steel. I have found that at the cold end, use of 304 ss improved the life of the air heater 2-3x over CS

RE: Tubular Airheater Design

Keep in mind A 513 is a structural material,the quality may not be consistant.

RE: Tubular Airheater Design

Bjaffa,

In terms of the operation, having a thicker tube wall will decrease the ID of your tubes, reducing the total surface area available for gas flow.  Since air heaters are designed with some extra surface area to allow for tube plugging, there shouldn't be a problem.  By using those tubes, you reduce the flow area by 2.6%.  I've seen airheaters with almost 15% of their tubes plugged off.

D

RE: Tubular Airheater Design

That small change in wall thickness will not hurt heat transfer enough to warrant any discussion.  In large power boilers A513 tube is what is used except on the cold end.  Generally the most economical choice there is Cor-ten.  Structurally you will be adding some weight, so you might consider this.

RE: Tubular Airheater Design

if there is H2S in the gas , you would be better with duplex than an austenitic such as 304,provided there is no welding involved it would be straightforward

RE: Tubular Airheater Design

I do not have any experience with Cor-Ten in a preheater, but have had some in a scrubber -- Cor-Ten works great if there is no abrasion or other means that removes the protective oxide scale -- this is a coal-fired boiler, I would assume that some abasion would occur, which means Cor-Ten will fail quicker than regular carbon steel..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources