RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Hi.

Can anyone tell me is there a way that I can rig up a three phase motor in such a way that it can be used in a similar fashion to a car alternator.

The whole idea is to use the motor to absorb the output from a internal combustion engine, in a home made dynamometer set up.

I have seen a few projects on youtube where people have used a three phase motor as a generator, attached to either a petrol engine or another driving motor, but it appears that putting a heavy load onto the "generator" just stops it generating.

I intend putting quite a heavy load on it as I intend dragging a 50kW engine to virtually its stalling speed, so in that regard, the "generator / absorber / brake" would actually be being run over a range of RPM, unlike the youtube projects or other projects I have seen, where people appear to be aiming to run the generator at a specific RPM, so as to provide a stable supply. I have no need to stabilise the supply, since I just want to dump it off somehow, via some form of heating element I presume.

That being the case, I suppose unlike a car alternator, I don't really have any need to regulate the voltage output.

I don't really know very much at all about electric motors, but I was hoping that a predetermined load could be applied, so that as engine RPM increases, hopefully the load on the "generator" would increase, as the generator output increases, thereby creating its own terminal angular velocity so to speak.

Having a series of predetermined loads, (found via trial and error), might then provide various terminal angular velocities, enabling various engine RPM performance to be analysed.

Would there a be a way to do that practically or am I just being ridiculous, expecting a novice can achieve that?

I have a 75kW three phase motor at my disposal.

Thanks

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

This is being done all the time. I have run all sorts of dynos from little ten kW units to large MW+ brakes for Scania and Volvo Penta. The unwind reel on a winder works the same way. Braking the sheet to keep web tension up and delivers the brak energy to the grid. Trains that brake (modern electrical ones) do the same thing.

And guess what? What is a wind turbine? Yes - a brake that delivers energy to the grid. Mature technology and, as I said, used everywhere, all the time.

Connect the motor to a VFD with regeneration and just do it!

OK, you may need to read the manual. You may need to understand a little bit more about induction motors and frequency inverters. But it is doable and there is not an incredible lot of learing to do.

Probably lots of stuff on the net. GIYF.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Thanks Skogsgurra.

It's encouraging you say that it's easy, but forgive my ignorance.

I have been Googling the last five hours but I can't see any real examples of such, where I might get a clue where to start.

Could you please explain what a "unwind reel" or even a "winder" is.

I had a look on Google and I can't even figure out what that is.

Or "braking the sheet to keep web tension up".

That went straight over my head too.

Thanks

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Google regenerative dynamometer, because that is basically what you are building. You might need the distribution system owner's agreement to connect a large regenerative load - effectively a generator - onto their network.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Sorry to confuse you. An example (only partly shown) of a winder is here: https://encrypted-tbn1.gstatic.com/images?q=tbn:AN...

The paper wep is going from the mother reel seen to the right, taken over a few guide rolls and spread rolls and divided into narrower sheets just before the operator's knees.

The paper speed is often 1500 to 2000 m/min and the web tension (the force in the paper) needs to be controlled within a few percents or the slitters (the round knives) will not work properly and result in paper salad instead of neat rolls for the printing press.

The brake motor is usually in the 200 - 500 kW range.

But, mind you, this has nothing with a dyno to do. It just shows another application of a regenerative brake.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

MRSSPOCK; The motor you have needs to be "excited" which means power has to be provided to it, so magnetic fields can be formed, so IT can then generate. That's why the yTubers have problems, they want their motor to generate without supplying it some electrical energy to support its needs.

A VFD (Variable Frequency Drive) is a device to control the speed of an induction motor - like yours. If you get the correct style it will drive your motor flawlessly and conversely let your motor generate to its heart's content, clear down to speeds below your engine's operating speed.

Now, where "regenerative" models of VFDs come in is they can drive the power they receive from the motor back into the power supply the drive is hooked to. This saves you great gobs of energy money if you care. It also can cause some difficulties if your supply can't accept that much power. If you are going to be a "dyno shop" this is the only logical way to proceed. If you aren't going to be a dyno shop then skip the "regenerative" aspect entirely as it doubles the cost of the VFD.

Instead, use a standard VFD instead. A standard VFD operates exactly the same way as a regenerative VFD except it can't send the excess back to the power supply. It shoves the excess into a capacitor bank inside itself. The capacitor bank is fine for most cases when the motor briefly 'generates' like when it's told to come-to-a-stop. In your case you would be continuously driving energy into the VFD that will fill the capacitors completely in a second or two. The result would be the VFD tripping on overvoltage and losing all control. To prevent that, standard drives allow you to hook a specific large power resistor to its two "Brake Terminals". The VFD then shunts current thru the resistor to keep the level of charge on its internal capacitor below tripping voltage. You just need to keep the resistor cool.

So the VFD will provide the motor's needed excitation while allowing you to adjust the load the generator sees, and dumping the received energy into a big dc resistor. Solves all your electrical dydno issues.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Keith, a a 50kW engine will need a a 50kW resistor, probably more ("dragging a 50kW engine to virtually its stalling speed"). Such a resistor will probably cost about the same, or more, than the upgrade from uncontrolled to controlled mains rectifier with regeneration. It will also be problematic to cool it if the test shall be going on for more than a few minutes. Especially in the summer. Cooling is a lot more expensive than heating.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

There is that. It certainly depends on the test profile. I have lots of bar resistors I just toss into a pail of water. That works well for a few multi-second loads, not so well for anything longer, unless I add a running hose to the pail. :)

If one just wants to know the horsepower an engine can put out you only need a few seconds per test. If one wants to test the engine and its subsystems, like its cooling system, then you'd surely want the regen.

I suspect you could find non-regen VFDs all day on Ebay. Probably not so with regens.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Of course, you could skip the resistors altogether and use the water as a braking resistor. That is being done even today. Saw huge ones to start ore crushers in Kiruna iron ore mine not so long time ago.

That worked quite well since the current was AC. For DC, you will get gassing and depending on what you add to increase conductivity (must do, pure water doesn't work so well) you will start producing H2 and NaOH (if you use salt) or H2 and O2 (I think) if you use sulphuric acid. Huge amounts, that is very prone to explode if you don't keep them separate.

I vote for a regen VFD.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Wouldn't you get chlorine gas out of the saltwater? eeeuu.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

No free Cl2 to the best of my knowledge when it's used on AC...

A plant I worked in where decoupled 200 MW generators could be run as sychronous condensers had a 'pony' six-pole-set wound rotor induction motor connected to a five-pole-set generator for run-up purposes [coupled through the isolated phase bus before the units were synchronized]. The wound-rotor motor current was controlled using a salt-water resistor; even after performing two run-ups I never smelled a whiff of chlorine from the box.

CR

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Yeah, agreed with AC but was thinking DC. It's interesting even on the AC that the ions seem to take so long to form that they can't. I'd think the reaction would be way faster than 8ms or so.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

I've boiled off hundreds of gallons of water per day doing run in loading on a gen set for a week. I used plastic barrels and truck leaf springs as electrodes. Never a smell of anything. Just lots of steam and water vapour. On start up a used a clamp meter and shoveled in salt until I had the current that I wanted.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Yes, Keith. Chlorine if DC. Can be vented away. The NaOH stays in the water and gets quite nasty.

This brings up an entirely different topic, that of electrolysis in AC situations. The 8 ms mentioned by Keith (or 8.333..) causes electrolysis products to be lifted off the surface during one half-cycle and then deposited back during the next half-cycle. So, not much net electrolysis.

But make the liquid (water, mostly) stream and you get an entirely different situation. I had sludge pumps, driven by VFDs, whose shaft diameters were reduced to half (and then broke) by leakage currents from the VFD. The general wisdom said that there shouldn't be any electrolysis because of the AC. But the streaming water did it. BTW, they were made from titanium just to prevent this. Didn't help.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Thanks for all your replies.

@ itsmoked : Especially the very clear explanation. Thanks

Now it starts to make some sense.

This might seems a simple question, but can a VFD work with either an induction motor or an asynchronous motor?

I suppose I still need a VFD that is rated to deal with a 75kW motor, even although it isn't supplying the motor as such, but rather dumping the generated power?

Could you give me an example where such a big heat dump resistor might be employed?

I mean, where could I buy such a thing.

This will just be a hobby dyno, some the VFD regenerative option would really be a bit over the top in this instance.

Thank

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Cressall Resistors make loadbanks in the multi-megawatt range. 75kW is a baby. Mosebach are another manufacturer.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Your question "can a VFD work with either an induction motor or an asynchronous motor?" has a very simple answer: Yes.

The reason is that an induction motor IS an asynchronous motor - it is usually called an ASynchrouous Induction Motor, sometimes with the acronym ASIM.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Thankyou for your replies.

Forgive my ignorance since I'm learning this stuff from a high school book.

In that book it says that the asynchronous motor is synchronized with the input frequency, whereas an induction motor isn't i.e. due to the slip component I presume, i.e. the RPM never equalling the number of poles x the input frequency directly, but differing slightly.

The book I'm referring to is from the stone age, so is it possible that back then there was no such thing as ASIM?

I suppose what I'm asking is, is there such a thing as an induction motor which is ASIM, or was that only true many years ago?

Thanks

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
sorry: correction, last post should have read..

I suppose what I'm asking is, is there such a thing as an induction motor which is NOT ASIM, or was that only true many years ago?

Thanks

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Are you mis-reading asynchronous for synchronous? The speed of the latter is determined by supply frequency. There are a few different types of asynchronous motors other than the squirrel-cage induction motor although they are all pretty much obsolete or niche market nowadays. For example you will still find wound-rotor induction motors in service where their specific characteristics are required, but they are not commonplace.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

I agree with Scotty. I bet you read an "A" that wasn't there. Because synchronous motors ARE just that "synchronized".

And, you should only need a VFD capable of handling the 35kW of your engine. Wait for someone to confirm that since the motor you have will need more excitation current than a 35kW would.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

It is possible to select either synchronous or asynchronous operation mode from several modern VFDs. ABB and Siemens can do both. There are also SRM modes available in some (that new reluctance animal that is being introduced these days).

Synchronous motors with permanent magnets (PM in the designation) are getting more and more popular because they are (slightly) more efficient than asynch motors.

You should really make up your mind and check what kind of motor you are going to use before proceeding. If asynch, then just about any VFD will work. If synch - you will have to sort out the ones that can do it. Ask the salesperson. But it won't do to be vague. Must know first.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
You're A-bsolutely correct.

I added an "A" that wasn't there!

The best about it, I already know that a preceding A in Greek inverts the meaning.

A-muse literally means to NOT think - That's what I was doing when I read A-synchronous in place of synchronous!

I already have the motor, but the spec' plate has had all the details worn off, so I don't know what it is yet.

I know someone who does, but haven't got hold of him yet.

It's off a crusher.

Thanks for your patience.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Sorry not to trust you 100 percent on this one.

It is extremely unusual to see such a relatively small synchronous motor on a crusher. ARE YOU SURE that it is synchronous?

If it is, you either have slip rings, which you do not seem to have (no place for them on the NDE) or it is a PM motor, which I do not think that it is. So, the most probable is that it is an asynchronous motor.

If the nameplate is so worn that you cannot even read the speed or type of motor, then you are in deep water. If this really matters to you, and if you are not trying to get some weird entertainment out of this conversation, you should get the facts first. Then, we can give you the answers. But this kind of discussion is not at all what we (at least me) find amusing. Or, with your ethymology, it is actually what it is.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
@skogsgurra: I don't believe I said it was one or the other. I have no idea as yet, though from your comments it seems pretty certain it must be ASYNCHRONOUS.

I have to say, needing 35kW to excite the thing is beginning to put me off this solution.

Seems I can't use it unless I have a three phase installation, which makes it a bit impractical.

I'm not amused either since I learned that sad

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD



You have said this or that several times. Your last words (on 3 Mar 14 18:48) on this were "I read A-synchronous in place of synchronous!"

Now, the Magic: You do not need a three phase grid to run a VFD. But if you need more power than around 5 or 10 kW, then a single-phase grid may be a problem.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Sorry, I just meant I read it in a text book, not on the motor.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Since you are only going to use the 'grid' to 'excite' your motor you will only need a few hundred watts from it. The engine power will need be 'disposed of' by the resistor.

The resistor will need to be very robust as previously mentioned. Water cooling will get you a long ways. You might be able to use something like a 1kW or 2kW resistor instead of a 35kW resistor by simply dropping it in a plastic pail of running freshwater.

The key is keeping a twitchy hand on the engine throttle because if the resistor opens => the internal VFD capacitor would fully charge in probably 200ms => the drive will trip (essentially disappearing electrically) => the the engine would suddenly be completely unloaded => would seriously over-speed => possibly coming apart.

Dynoing engines is seriously dangerous. Go to YouTube and see the myriad disasters. This is why they are done in "test cells" without humans being immediately present.

Dyno tuning gone bad

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

(OP)
Sorry, I misinterpreted your comment,

"the motor you have will need more excitation current than a 35kW would."

I thought you meant I needed 35kW to get it excited!

Maybe I should stay clear of such a powerful 3 phase project if I don't know more fully what's going on, lest I become the smoking resistor.....

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Like a lot of tasks your project is not very hard or complicated to people who understand the systems and their operations. Undertaking all of it with no working knowledge of even the subsystems can certainly be daunting.

Caution is the better part of valor. No one here, in this forum for professionals, will be trying to talk you into what's actually a pretty complex project fraught with various, um, shall we say, energetic problems.

Getting out-of-the-box might help you to a solution you haven't contemplated. Why do you want to dyno an oddly middle-of-the-range engine in the first place? That's like an industrial rated 4 cylinder or a steroided 2 cylinder. Automotive 4 cyls put out way more than 50hp these days. Will it be an on-going regular occurrence? Is it a critical need? Just entertainment? Compliance testing? Give us more info and we might be able to suggest alternative solutions to your situation.

Keith Cress
kcress - http://www.flaminsystems.com

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

May I throw in a question?
Given the close relationship between motor torque and motor current, should the VFD be sized for maximum torque rather than HP?
I wonder what the VFD sizing should be based on at times when the motor is regenerating at greater than rated speed?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

Then you have another set of options.
If you just run, you are in constant power territory. Maximum available braking torque then falls after you have reached rated speed (because of the constant voltage and hence falling V/Hz).
You can move that speed up from 1800 or 3600 RPM to around 3120/6240 RPM by connecting in Delta instead of Star. Or you can throw in a transmission and have any speed range you desire.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RUN THREE PHASE MOTOR LIKE CAR ALTERNATOR - VARIABLE RPM - VARIABLE LOAD

You have lots of good tech data on how to do what you want. So thought I would add ballpark prices for reference.

A 35kw continuous rated regen resistor will come in at about 3' x 3' x 5' in size. I have one our guys speced wrong so know :) Takes up a lot of shelf space collecting dust....

Since we supply typically 10-20kw resistors with our large spindle drive systems, I would swag for you the price for a new 35kw is around $ 3000.00 for an air cooled one (no fan, no water cooling).

And for reference, a new vfd to do this is typically around $ 7,000-10,000.

www.KilroyWasHere<dot>com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close