Hello Everybody,
I'm working on a tank-farm fire water system. I like to know where to locate the deluge valve.
Is there any code or standard that specify appropriate location for a deluge valve assembly systems?
Can I locate about 14 numbers of deluge valve systems in one location.
Thanks for your upcoming response.
boboattah
I'm working on a tank-farm fire water system. I like to know where to locate the deluge valve.
Is there any code or standard that specify appropriate location for a deluge valve assembly systems?
Can I locate about 14 numbers of deluge valve systems in one location.
Thanks for your upcoming response.
boboattah





RE: Deluge Valve Assembly location
Travis Mack
MFP Design, LLC
www.mfpdesign.com
RE: Deluge Valve Assembly location
RE: Deluge Valve Assembly location
Travis Mack
MFP Design, LLC
www.mfpdesign.com
RE: Deluge Valve Assembly location
We could refer also to NFPA-15 if the deluge valve is for the water spray system which indicate in clause 6.3.1.4.1 - system actuation valves shall be as close to the hazard protected as accesibility during the emergency will permit.
One way to do it is as mentioned by travis mack in which blast wall is provided safe distance is concern
hope it helps,