NEC/OSHA Clearance Around Enclosed Machine

NEC/OSHA Clearance Around Enclosed Machine

NEC/OSHA Clearance Around Enclosed Machine

(OP)
I have a 120V (plugs into outlet) "wafer wash" machine (2ft x 3ft) with electronics etc fully enclosed with casters (too roll out for service). When operating, verything is fully sealed (like a dishwasher).

One of our maintenance guys says I need a 3-ft clearance all around per NEC/OSHA.
But I think that applies to exposed/live wires, breaker panels etc -not an enclosed machine.

Any advice would be appreciated.

RE: NEC/OSHA Clearance Around Enclosed Machine

The 3-foot clearance is NEC 110.26. It is a working clearance for working, examination, adjustment, etc. If this is some type of machine where it is normal that an individual must work on it, then he may be correct. You may need the 3-foot working clearance in front of any access panel, etc.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources