Greetings
For grease (kitchen exhaust) ducts, can intumescent coating be used on the outside of of the duct instead duct wraps like Fyrewrap? How much clearance to combustibles will be required if that is the case? This is for compliance with NFPA 96.
Much obliged for any information.
For grease (kitchen exhaust) ducts, can intumescent coating be used on the outside of of the duct instead duct wraps like Fyrewrap? How much clearance to combustibles will be required if that is the case? This is for compliance with NFPA 96.
Much obliged for any information.





RE: NFPA 96
RE: NFPA 96
RE: NFPA 96
www.fireduct.ie/Galloway%20Brochure%206pp.pdf
I realize its tested to another standard and I'm not trying to compare standards. Why are these paints not suitable for grease ducts compliance to NFPA 96 as you say?
RE: NFPA 96
RE: NFPA 96
Intumescents have other issues like preparation of the substrate, required thickness, quality of the application, skills of the applicator, etc. I wouldn't approve it my jurisdiction unless I was presented with some very compelling information.