NFPA 96

NFPA 96

(OP)
Greetings

For grease (kitchen exhaust) ducts, can intumescent coating be used on the outside of of the duct instead duct wraps like Fyrewrap? How much clearance to combustibles will be required if that is the case? This is for compliance with NFPA 96.

Much obliged for any information.

RE: NFPA 96

Have to look at. 96. More than likely No!!!

RE: NFPA 96

There is no mention of intumescent coating in 96. Are there any intumescent coatings that meet the requirements?

RE: NFPA 96

(OP)
No, there is no mention in 96 for Intumenescent paints. But ducts with these paints are tested for fires inside and on the outside and are rated for 2 hours. See this link as an example:
www.fireduct.ie/Galloway%20Brochure%206pp.pdf

I realize its tested to another standard and I'm not trying to compare standards. Why are these paints not suitable for grease ducts compliance to NFPA 96 as you say?

RE: NFPA 96

Would say the shaft or wrap is protecting in case the fire gets out of the duct and not fire attacking the duct

RE: NFPA 96

It wouldn't be recognized by most U.S. fire officials because the testing lab is probably not recognized and would be challenged. NFPA 96 doesn't excluded foreign test labs but the data sheet is based on British standards. The fire-resistance requirements in the US are based on ASTM E-119.

Intumescents have other issues like preparation of the substrate, required thickness, quality of the application, skills of the applicator, etc. I wouldn't approve it my jurisdiction unless I was presented with some very compelling information.

RE: NFPA 96

(OP)
Thank you for the information.

RE: NFPA 96

You'll have to stick to metal ducts of particular gauges predicated on duct dimensions.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources