fresh air load calculation
hai to all,
I am new to this site and I have one doubt please help me..
Imagine a non-conditioned room, and I am supplying 1000cfm of fresh air at 18 degrre.
I want to know how much heat load will take that fresh air ?
RE: fresh air load calculation
read some fundamentals.
? How much heat load that fresh air has to be removed?
What dew point do you have to what do you want at what temperature to end up with; as in first reply...?
let me make it more clear. I know it is depended to lot of if's and but's.
I have a kitchen. the total heat load calculated for that room is say 10 ton.
the thermostat set point taken as 24 degree. Now I am supplying 1000 cfm of fresh air @ 18 degree.
I think it much more clear now. I want to know is there is any direct calculation for finding out the load taken by the fresh air?
Basically, you don't have a clue about HVAC and you want us to design you a solution.
q: heat transfer rate, Btu/h
Trt: Room temperature, F
Tst: Supply Air temperature, F
V: Air flow rate, ft3/m
q= 1.085 x V x (Trt - Tst)
Metric form:
q: Watts
V: L/s
Trt, Tst: C
q = 1.2 x V x (Trt - Tst)
Note this calculation is based on sensible heat and it is used for dry bulb temperature while not taking into consideration the latent loads or moisture sources.
Thank you for your valuable information. it is clear now.
For me it is a part of my learning curve. I believe that I will be always junior when it comes studies.
And I prefer continuous learning until my last breath.
There is no bypass to basic learning, which in this case means - psychrometrics.