Extending header/main through a building for additional risers?
6" combined service into a large building, domestic takeoff, fire protection through a double check valve to a header with a few risers. Is it OK to take a 6" right off the header through the building to locate some more risers on the other side of the building?
RE: Extending header/main through a building for additional risers?
It should be ok as long as it is downstream of the double check valve and is sized for the flow/pressure requirements of the entire system per NFPA 13 and/or 14.
Would suggest do it after the flow switch or add a flow switch shortly after the tee
In care there is a leak/ break between the tee and the added riser
Yeah. Make sure you are after the double check valve. As mentioned above, I would have a flow switch on the bulk piping just to monitor for large leaks. Just consider it insurance or something.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
I'm assuming both buildings are on the same property - correct?
One large building.