System Bonding Jumper for Separately Derived System

System Bonding Jumper for Separately Derived System

System Bonding Jumper for Separately Derived System

(OP)
To All,
A contractor is installing a single phase 120/240 volt service supplied by a small (25 kVA) indoor 480 Volt to 120/240 Volt transformer at one of our sites. From what I understand, that is considered a separately derived system by the NEC. As such, it much have a system bonding jumper per Article 250. There are two places that this jumper can be installed: one is at the neutral point of the transformer, and the other is at the neutral bus in the circuit breaker panel. Is one location for this bonding jumper preferred over the other?
Regards,
Dave

RE: System Bonding Jumper for Separately Derived System

In your case I'd say the panel as that is the most common and expected location for a typical low voltage service.

Keith Cress
kcress - http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources