Stair landing concrete-filled pan design

Stair landing concrete-filled pan design

Stair landing concrete-filled pan design

(OP)
I am designing a stair for a fabricator. The intermediate landings are constructed of a 3" slab poured into 12 gage metal pans. The pans span 54" and are "U" shaped sections 18" wide with 1.5" upturned legs. I was assuming that the upturned legs would be fully braced by the slab and that I'd compute the flexural capacity of the pan alone (ignoring the strength of the concrete since there is no flexural reinforcing in the slab). The gage metal pans are not close to working. I am not sure what I am doing wrong. This may be one of those things where a miscellaneous metals fabricator "has been doing it this way for years", and now here I am telling him that it doesn't work. Can someone enlighten me on how concrete-filled pan landings are designed? Thanks.

RE: Stair landing concrete-filled pan design

(OP)
Just found the answer to my question. There is a publication called the NAAMM AMP510-92 Metal Stairs Manual that is available for free download. In that manual are load tables for various types of pans. My calculations were correct. The pan construction that the fabricator wants to use does not work.

RE: Stair landing concrete-filled pan design

Good checking.

RE: Stair landing concrete-filled pan design

cliff234...exactly!
You can take the opposite approach and consider the pan to be only a form and reinforce the concrete.
If exposed to weathering, warn the end user that lack of drainage will cause the pan to corrode. If you reinforce the slab, you won't have to worry about that as long as you have adequate edge support for the slab.

RE: Stair landing concrete-filled pan design

These systems inevitably rust out when exposed to weather - especially if de-icing slats are used.
I would add re-bar as well as a back up when portions of the pan dissolve.

RE: Stair landing concrete-filled pan design

I agree with a2mfk - floor deck it the way to go

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources