I am having a difficult time in figuring out the best way to recover heat from drying process.
The basical idea is - heat is supplied to drying line, where gras is dried. Thhe hot and moist air from grass is collected and through heat exchanger cooled down. The fresh air for burning process (biomass burner) is pre heated with the exhaust air from grass drying (HE mentioned above).
Air flow volumes are quite large, ~30 000 m3/h. Temepratures are Fresh air ~15C, air from drying process ~80C.
What would be the best way to do this?
This probably ir the most efficient way to do this http://www.energydepot.com/RPUcom/library/images/M... , but then I am thiking about the tubes... finned.. dimpled.. other?
Any suggestions would help, thanks!
The basical idea is - heat is supplied to drying line, where gras is dried. Thhe hot and moist air from grass is collected and through heat exchanger cooled down. The fresh air for burning process (biomass burner) is pre heated with the exhaust air from grass drying (HE mentioned above).
Air flow volumes are quite large, ~30 000 m3/h. Temepratures are Fresh air ~15C, air from drying process ~80C.
What would be the best way to do this?
This probably ir the most efficient way to do this http://www.energydepot.com/RPUcom/library/images/M... , but then I am thiking about the tubes... finned.. dimpled.. other?
Any suggestions would help, thanks!





RE: Low temperature air-air heat exchenger
TTFN

FAQ731-376: Eng-Tips.com Forum Policies
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
RE: Low temperature air-air heat exchenger
And of course I would like to keep the HE as small as possible, but the size isn't the main argument here.
RE: Low temperature air-air heat exchenger
These types of heat recovery units have a few problems. First, the operating pressures are near atmospheric on both sides, allowing for very small pressure drops on both sides of an exchanger. Low pressure drops, generally translate to low heat transfer coefficients. The second problem is that the available temperature difference is very small. These factors combined result in realatively huge exchangers for the amount of heat recovered. The payback for this type of exchanger is generally extremely long.
Since the heat transfer in both fluids is low, fins are of no help. The better choice is either bare tubes or plate-type exchangers. In either case the econimics of these are pretty awful.
Regards,
Speco
RE: Low temperature air-air heat exchenger
RE: Low temperature air-air heat exchenger
I wish I knew. I've never seen a project of this type actually go forward. Here are a few ideas to get you going. Let's assume an overall U value of 6 btu/(hr-deg F-Ft^2). This is approximately 34 W/(m^2 deg K) Calculate the heat you are trying to recapture. Calculate a log mean temperature difference using the resulting four terminal temperatures. From that, you can obtain a required surface. Assume some value per surface area (maybe on the order of $50/ft^2). That's just a guess. The larger the surface the smaller the cost per unit area. You will quickly get an idea of how much it costs to recover any quantity of heat. The exchanger will only be a portion (maybe half) of the installed cost.
As an alternative, you might try contacting a few vendors of this type of exchanger.
Regards,
Speco
RE: Low temperature air-air heat exchenger
I only put it that way because with ground-loop NO Heat Pump process cooling in 50f soils, I have circulation numbers and differences for both pre-heating and pre-cooling air +/- 7f or more different than of those 50-52f soil temps I have.
This is a ground loop of tubing is 1" dia PE3408 dr-11 and circulated fluid from water to 34% p-glycol is used. Earth-Coupled to Air exchanges, near 12 months a year, like a solar collector-
just an Earth-Collector / Rejector (ECL: Earth Coupled Loop)
Some 7ft deep x 2ft wide to 32" wide ditches in damp clay transfer with three 3/4" PE lines [over at 5ft + under at the 7ft, of 6 pipes in a cross-section view], about 100 btuh per foot, rejected heat as a sink, and absorbing from those same ditches as then a "source" at about 70 to 80 btuh/ lin-ft [ 500ft piping is over-under straight in up to 240ft ditch length, per. ]
RE: Low temperature air-air heat exchenger