Substation Lightning Protection

Substation Lightning Protection

Substation Lightning Protection

(OP)
When performing a lightning shielding study for a transmission substation do you consider the power transformer winding BIL or bushing BIL in your study?

RE: Substation Lightning Protection

Is this an either/or or a yes/no question? Normally, the winding BIL and bushing BIL are the same. Yes, they need to be considered. If different, use the lower BIL.

RE: Substation Lightning Protection

(OP)
A lot of times the bushing BIL will be higher (in contaminated areas) so I wasn't sure if the winding BIL when lower would need to be considered. If there is a strike and a voltage wave is propogated down the bus to the transformer it will reflect back due to the impedance of the transformer. I wasn't sure if that wave would make it into the windings and as such the winding BIL would need to be considered.

Sounds like it does?

RE: Substation Lightning Protection

No.
BIL is associated with travelling waves.
shielding is associated with lighning strokes.

RE: Substation Lightning Protection

Shielding is dependent on BIL because higher BIL equipment can withstand a higher current surge. A higher current surge is associated with a longer strike distance. A longer strike distance can be shielded with less shieldeing.

RE: Substation Lightning Protection

jghrist,
higher BIL equipment can withstand a higher voltage surge . A very high surge current crossing an equipment, with nanosec of duration, is not a problem!

RE: Substation Lightning Protection

Voltage surge = stroke current times surge impedance.
See page 37 of 7anoter4's link.

RE: Substation Lightning Protection

Let's go back!

Question:
When performing a lightning shielding study for a transmission substation do you consider the power transformer winding BIL or bushing BIL in your study?

Answer:
No.
equipments BIL is associated with travelling waves.
shielding studies are associated with lighning strokes and busbar BIL.
In EHV substation if a lightning strikes the transformer it will explode!
In EHV substation if a lightning strikes the bus, a CT, PT or arrester will explode!
Shielding wires or masts are devices to deflect lightning strikes on substation equipments.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources