Part-winding connection

Part-winding connection

Part-winding connection

(OP)
Hello,

How is called this connection


I found it on an semi-hermetic compressor it is used for "part-winding start".

How does it work?
Any information on it will be great

www.eldvigateli.com

RE: Part-winding connection

This appears to be a unique, in my experience, example of a two speed, one winding connection. The 'unique' portion is the presence of the additional winding sections that extend from the center of the traditional delta to comprise the 2U, 2V, and 2W connections.

My guess is that when power is applied to the 1U-V-W connection that the result is a two pole connection and that when power is applied to the 2U-V-W connection that the result is a 6 pole connection. Presumably the 6 pole connection would be energized first for starting and the the 2 pole connection would be energized second for running.

If you can provide a picture of the portion of the schematic that shows the starter as well as the specific rating(s) of the motor for starting and running then the answer to your question may be more apparent.

I hope you find this answer helpful. Please respond with more information.

RE: Part-winding connection

(OP)
Hello,

This is the schematic that is on the temrinal cover.


This is the nameplate:


Thanks

www.eldvigateli.com

RE: Part-winding connection

I agree with rhatcher's guess. Interesting design - I haven't seen that winding configuration before.

If we get a confirmation of those answers it might be the basis of an interesting interview question for the future, just to test a candidate's ability to apply logic and reasoning to something unfamiliar. smile

RE: Part-winding connection

If it is 2p & 6p then why does the nameplate list 4p and only 4p? and dual delta windings?

'part winding start' is just normal u/v/w in delta
'direct start' adds another delta across same u/v/w but 60 degrees out of phase....

each regular delta coil has 60 degrees across it for 120 degrees from u to v to w. aAding the 7,8,9 wires puts 180 degrees across each of those coils... wierd.

Being a compressor, I am guessing it runs in the 'partial' mode but somehow the added coils reduce inrush for starting with those phase shifts?

www.KilroyWasHere<dot>com

RE: Part-winding connection

(OP)
It is not a double speed motor.This is for sure

The first photo which I shared (http://i.imgur.com/tFQ8go8.jpg) is from completely different source - the book "Winding technique of electric motors" by Neven Srb. But unfortunately there is only this schema and nothing explained :( Except that this is a kind of "part-winding start"

www.eldvigateli.com

RE: Part-winding connection

(OP)
Sorry!!! checked again, this schema is given exactly in the "Pole-changeable windings" section of Neven Srb's book!

So it is very possible that @rhatcher is right!

Tomorrow the motor will be cutted-off and winding striped out, I will try to draw the winding diagram.
And I will appreciate if someone who can better read the copeland diagram to try to explain how exactly this thing works.

For now it is a "part-winding, pole-changable" motor, correct?

www.eldvigateli.com

RE: Part-winding connection

that didnt work.... dont know how to imbed small pix. page 7 of last doc says the paratwinding is optional to reduce starting current.

www.KilroyWasHere<dot>com

RE: Part-winding connection

Hi,
I haven't had time to verify it but I'm pretty sure I've seen that connection on a dual voltage 230/460 volt delta connected motor. The connection that you show was used to run the motor on a 575 volt circuit. 1, 2, 3, were lines, 10, 8, 5 were together as were 11, 9, 6, and finally 4, 7, 12. If you draw it out I think you'll see it looks like what you have above.

Thanks

RE: Part-winding connection

That's a 2 delta PWS. According to the name plate and schematic.

Here is the connection diagram to rewind this motor.

RE: Part-winding connection

(OP)
Thank you very much @Motorwinder!

One more hint please:
How to read "Coil end No"?
1 is the beginning of the first coil and 2 is the end of the first coil
3 is the beginning of the second coil and 4 is the end of the second coil
5 is the beginning of the third coil and 6 is the end of the third coil
...and so on...

Is this correct?

www.eldvigateli.com

RE: Part-winding connection

Each number represents a group start and finish.

Glad I could help.

RE: Part-winding connection

This might help

Regards

RE: Part-winding connection

(OP)

Today we started to open the connection of the motor. The strange thing which is different from the first picture which @MotorWinder showed (4 pole, Delta connected, Part winding, Adjacent Pole, 2 Circuit), is that there are connections with 3 leads.
The other strange thing in this point (where 3 leaads are connected together) is that one of the leads are with 6 wires, the other two leads are with 3 wires
Please check the photo bellow



www.eldvigateli.com

RE: Part-winding connection

That would possibly make sense: the winding connected to terminals 7,8,9 sees full line current, so that would be six strands. The other two windings carry lower current and are wound with three strands, e.g. the current entering at terminal 7 splits between the windings connected to terminals 2 and 3.

RE: Part-winding connection

Looks like a pole connection.

Please post all winding data, IE: Total number of coils. Wires in hand, wire sizes, number of wires to each lead, number of turns, number of total wires in slot. Coil pitch (span).

Iron dimensions: Length, tooth width, back iron(iron below slot), bore diameter, slot depth, number of slots. Number(if any) air ducts.

I can help you sort this out. Just need more info.

RE: Part-winding connection

Hello Elin

Take care with this kind of connection, this is sure a Part Winding but you have manny of this one, the exactly connection most come from the original winding connection, this kind of hermetic compressor manufactured in europe usually are designed for one third/two third connection.

Regards

Carlos

RE: Part-winding connection

1/3, 2/3 only on a 6 pole.

RE: Part-winding connection

Quote (Motorwinder)

1/3, 2/3 only on a 6 pole.
If you thought because four pole winding can not be made ​​with 3 parallel circuits, you are wrong.
Lot of 4 pole, PWS windings are done with 3 absolutely symmetrical circuits.
But, I think here is not that case.
http://winding.wix.com/design

RE: Part-winding connection

(OP)
Hello,

Thank you for your replies!

The winding impregnation is very hard and it is very dificult to take the connection, that is why we are so slow


This is the correct position of the coils:


The strange thing is that from the same slot and coil goes out two "coil end"
Other strange thing is that there are "pole connections" with three "coil ends" - 2 with 3 wires & 1 with 6 wires

www.eldvigateli.com

RE: Part-winding connection

I will have to retract my guess on this winding being a two speed. Since there is no shorting contactor in the controller, this is not a two speed, consequent pole, winding.

I think ScottyUK is correct. The connection point with three coils ends occurs at the point where the winding segments 7,8,9 join the center of the winding segments 1-2, 2-3, and 3-1. The coil end with six wires is for the winding segments on terminals 7,8,9 and the other two coil ends with three wires are for the split in the center of winding segments 1-2, 2-3, and 3-1.

Further, I think that the pole groups with two coils come into play for the winding segments 7,8,and 9. Specifically, the outer coils in each of these groups make up the 7,8,9 segments with the two outer coils of opposite pole groups being connected in parallel to form the 7,8,9 segments.

If so, the coil ends with six wires will split into two leads of three wires each going to the outer coils of opposite, two coil, pole groups. The other ends of the outer coils will connect to each other to form leads 7,8,9.

The result is a four pole winding for both start and run with the start connection having additional winding segments added into the circuit to reduce the starting voltage across each of the run segments. This, of course, reduces the overall starting current.

I will conclude by saying that I have not seen this connection before. It is similar to the combined wye-delta connection mentioned by startkopete but it is certainly not the same thing. This being the case, my ideas about this winding are simply an educated guess. ElinBG should proceed with great care in taking connection data, counting turns of all coils, and carefully measuring wire sizes.

RE: Part-winding connection

Interesting analysis rhatcher. The physical arrangement diagram helps immensely with understanding. I too have never seen this winding configuration.

RE: Part-winding connection

A phase =black
b phase =green
c phase = red
6 groups of 2
6 groups of 1
2 delta PWS

sorry for the bad paint shop job..

RE: Part-winding connection

RE: Part-winding connection

I spotted a mistake in my first two drawings. It was late when I drew them out..

This should work for a 2 delta PWS with that coil configuration.

zlatkodo, please double check.



RE: Part-winding connection

Hi, Motorwinder,
1. - Your last drawing, conditionally speaking, is correct.
Obviously, an EASA's double-layer patern is converted to single-layer.
But, this pattern has a significantly increased content of harmfull harmonics (please, see the chart here) because of asymmetrical field distribution in the startup phase, in which only the first part winding is connected, since only some of the slots are magnetized.
Sometimes, this harmfull content could prevent complete startup of the motor. I think, this connection is not suitable for refrigerant compressors, at all. Frankly, I think that these PWS connections ( both: single or doble-layer) are not suitable for any motor.
2. - One more thing. The diagram you suggested do not match what is described on the original winding. Therefore , there is a " turns / coil " issue . As is well known any redesign of winding causes a change of " turns / coil " ( or check, at least ) . In order to do that job , you need to know all the parameters of previous winding ....... And so on..
Obviously , the best and easiest solution is to record the original winding.
BTW , in this case, I think, it is about the two one-layer windings in the same slots with no intermediate insulation between them . Turns/coil could be the same or different.

http://winding.wix.com/design

RE: Part-winding connection

(OP)
Hello,

I finnaly opened the winding.
Actually you can count kind of 24 coil groups, instead of 12.
They are placed as you see them in the picture, one above the other. All the connections are as in the picture but the coil ends are splited for the part-winding.

www.eldvigateli.com

RE: Part-winding connection

What an interesting and informative discussion this has been - thank you to all. smile

RE: Part-winding connection

peeking in on this thread due to its many replies

Indeed as ScottyUK writes, “What an interesting… discussion…”

11 Feb 14 17:41 post by Motorwinder requested “…number of slots.”

First off;

Scrolling among all the posts… the actual number of slots in the stator has not been declared.

(If I missed where that was posted, I’ll plead guilty.) I’m scrolling back to double check.

HOW MANY SLOTS ARE IN THE STATOR?

The designer/manufacturer of this winding incorporated a “delta” connection within the middle
of a “Y” connection for the partial energizing of the device/slash/electric motor winding.

This arrangement adds additional resistance to the motor circuit reducing current etc. for starting purposes.
Ingenious… and we all wish we had thought of it. (huh!)

In the end, a competent motor winder will replace, insert, and replicate whatever winding data
is extracted from a particular device or piece of equipment, and replace it all accordingly.

I vote for… [Putting the winding back, the way you ‘found’… find/extract it], correct any mechanical
issues with the motor (if any) and return it to a valued customer.

Always enjoying the forum,

John

RE: Part-winding connection

Hello All

I am in agree with dArsonval. The post start with a wrong winding diagram, this drawing belongs to one two speed one winding motor (dahlander),and post sayd Part Winding, later we have receive a semi-hermetic compressor name plate and exetrnal wiring, both belongs to part winding motor. Then we have been wondering if this connection or the other one.....,
in this cases all technicians involved in this kind of problems knows the most important are winding information, if we don´t have it then we need to calculate the winding.So slot number, groups, turns, coils per group, span and core sizes are important.

So I am still no convenced elin has the right connection, The last motor winder diagrams shows a 36 slot stator, 12 groups, 8 groups of 2 coils (SPAN 1-8, 1-10) and 4 groups of one coil(SPAN 1-8). Now Elin sayd 24 groups, I can´t see the picture with 24 groups arrangment, is not usual you can connect 24 groups for 4 pole ( the usual is 12 groups or 6 groups), I think are 24 coils, but......


Regards

Carlos

RE: Part-winding connection

(OP)
Hello all thank you for your answers!

The motor is exactly as you said 36 slot stator, 12 groups, 8 groups of 2 coils (SPAN 1-8, 1-10) and 4 groups of one coil(SPAN 1-8)

I said that you "can count" 24 groups, because the coils are kind of "doubled".
For example: From slot Number 2, are going out 2 coil leads (No 1 & No 7) and so on ...
I am very busy these days but I will try to upload the correct diagram this evening and will wait for your opinions.

www.eldvigateli.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources