Twisting of 1-Phase Branch Circuits

Twisting of 1-Phase Branch Circuits

Twisting of 1-Phase Branch Circuits

(OP)
Today I was looking at the as-built drawings for a physics lab that is adjacent to a lab I will be renovating. I noticed on the electrical plans that the engineer provided isolated/insulated grounds to all the receptacles and also called for the branch circuits to be twisted with a twist rate of 4" per twist cycle.

Now my fundamentals of electric theory and communications may be a bit rusty, but every time I have read about twisted pair it had to do about common-mode noise reduction with differential mode signaling. The reason for the twisting, as my understanding goes, is twisting having both wires be equally affected by the incoming interference. Since the signal is differential, when the receiver subtracts the two signals the noise gets cancelled out since it (hopefully) has the same magnitude and phase on both wires.

Lately I have heard some people thinking that twisting of the feeders will help reduce emitted RF interference from AC feeders/branch circuits. When it comes to 3 phase, I think this will only help marginally since each phase is 120degrees out of phase and should cancel. I guess twisting could help get the cables closer together which could help keeping the emitted EM at 120degrees out of phase with each other helping them to cancel out?

In my opinion, running the feeders/branch circuits in grounded steel conduit is the best way to reduce EMI.

I guess my questions are:

1. Will twisting the wires in a branch circuit actually cause more trouble than good? I mean twisting the wires would increase the inductance which would increase any mutual inductive coupling between adjacent twisted branch circuits run in the same conduit?
2. Would twisting the wires increase the inductance and possibly cause higher voltage transients from switching or loads coming on/off on the circuit?
3. Would twisting provide any benefit to decreasing emitted RF interference from a single phase branch circuit?
4. Do 2 wire parallel branch circuits emit RF interference?

As always, thanks for any info you can shed on the subject.

DJR



RE: Twisting of 1-Phase Branch Circuits

A hot and a neutral to a receptacle is a single phase application regardless of possible origin in a three phase panel. The twisting tends to neutralize induced 60 Hz noise in nearby sensitive circuits.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Twisting of 1-Phase Branch Circuits

It's about the tiny loops of wire made by the twists intercepting magnetic fields. Any intercepted fields add or subtract from the instantaneous current flowing in the circuit causing noise. When you twist them adjacent twists will present opposite additions or subtractions - thereby cancelling the coupled in interferences.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Twisting of 1-Phase Branch Circuits

At 50 or 60 Hz, the only significant effect of twistng branch circuit conductors will be to increase costs.

RE: Twisting of 1-Phase Branch Circuits

In a physics lab it's likely got nothing to do with 50 or 60 Hz.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Twisting of 1-Phase Branch Circuits

60 Hz fields cause big problems when making very sensitive measurements. The physics lab may very well be constructed as a large Faraday cage.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources