Reyroll 2B3 High Impedance Earth Fault Relay

Reyroll 2B3 High Impedance Earth Fault Relay

Reyroll 2B3 High Impedance Earth Fault Relay

(OP)
Hi
I am working on Reyroll 2B3 High Impedance Earth Fault Relay. The information i got that relay is fixed at 20mA with Voltage setting form 15V to 250V. I have to present the characteristic of this relay on time current characteristic Graph. Could anybody please tell me that how i can show that on TCC?
Regards
SRA

RE: Reyroll 2B3 High Impedance Earth Fault Relay

Why would you want to show it on a TCC? It's an instantaneous - in so far as anything is instantaneous - unit protection relay. You wouldn't normally expect it to coordinate on a time / current basis with anything else. If there's an in-zone fault greater than setting current it trips immediately, otherwise it remains stable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources