I have a project that requires a 3-hour horizontal assembly between the 1st and 2nd level and the 1st level is type IA construction. I have assumed that to meet this requirement I would need to design the floor framing system with the primary framing members as 3 hour rated and the secondary members would be 2-hour rated as listed in IBC Table 601 type IA.

The architect of record is insisting that a "3-hour Horizontal Assembly" must have all elements with a 3 hour rating.

Do I need to provide 3-hour rated concrete joists in addition to the 3-hour girders and columns of the primary framing system and slab in order to meet this requirement?

RE: 3 hour horizontal assembly

Which edition of the IBC is adopted by the jurisdiction?

RE: 3 hour horizontal assembly

(OP)
This project will be designed in conformance with section 510 IBC-12 and required a 3-hour rating due to area limits. The assembly is deigned as a thermally restrained 3-hour assembly as follows.

Primary structural frame is prestressed inverted T beams on precast columns. These members are the primary structural framing and will be designed to 3-hour.
The secondary framing members are Prestressed double T joists with cast-in-place topping. The deck will be 2½" DT flange with 3½" CIP reinforced structural topping. Total depth of deck is 6" for +3-hour rating. My intent is to design the DT stems as un-restrained 2-hour beams in conformance with IBC Table 601 Type IA for secondary framing members per MNL-124 rational analysis. These members meet the requirements to be designed as restrained but I am opting to use an un-restrained design to be conservative.

ASTM E119 allows the test for a restrained assembly to continue for a period up to twice the hourly un-restrained rating of the beams as long as the unexposed surface does not exceed 250º above ambient. This means that the beams in a 3-hour restrained assembly must have 1½ hour un-restrained beams minimum. IBC Table 601 limits this to 2-hour for the secondary members.

RE: 3 hour horizontal assembly

Based simply on equivalent thickness, and assuming siliceous concrete, your design complies with 2012 IBC Table 722.2.2.1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources