I recently came across a double ended 480 service entance switchboard with both mains closed and the tie open. surge protection is installed on both service entances. Each surge protector is equipped with a surge counter. The surge counter from one substation recorded around 10 surges, the other counter indicated over 300. I reset the counters and checked back a month or so later. I found one counter showing only a handful of surges and one showing hundreds. Both services are supplied by dry type transformers fed from an entirely underground system with multiple levels of surge peotection and some high end meterng that would have picked up any surges on the distribution system. Essentially I can rule out any causes external to the building. The building only has 'typical' commercial building loads, motors, lights, etc... No low voltage pf corection, transformers tapped at nominal. Any thoughts on what could be the cause? This isn't the first tim. I have seen this either. Several other buildings in the area have similar installations and show the same problem.


Thanks for your help.

RE: Strange Readings from Surge Counters

Have you considered interchanging the surge counters? That will tell you if there is really are that many surges or if you have a surge counter that is malfunctioning.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Strange Readings from Surge Counters

If there are VFD's or solid state rectifier's or U.P.S. systems in the area on this feed they will generate lots of voltage spikes.

RE: Strange Readings from Surge Counters

(OP)
There would be many vfds on both services. Why would vfds produce voltage spikes at the service? The only voltage spikes I am familiar with vfds producing is on the output side. They wouldn't show up on the source side.

RE: Strange Readings from Surge Counters

check surge counter installation. Both must obbey procedure of comissioning.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources